|
Yes, this is a known problem. The sizing routines don’t know about the DOAS, nor how it will eventually operate. The easiest workaround is probably to use OtherEquipment to provide internal gains that account for the missing DOAS. Use the schedule day types so these loads only happen during design days. You’ll have to figure out the thermal load from the DOAS in Watts, using mass flow rate times specific heat of moist air times temperature difference between DOAS supply and zone air. For cooling use negative value for internal gain. From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Sorry. Let me reiterate. When I use two systems, energy plus cannot meet the load most likely because it didn't size them correctly. If with one system, auto size will work correctly and properly size it to meet the load.
__._,_.___ Posted by: "Brent Griffith" <Brent.Griffith@xxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |