Dear All,
I was modelling a solar desiccant with evaporative cooler air conditioning system using EPlus. The Input IDF file, System Diagram and Plant Loop Diagram are attached below. I encountered the following errors when I run the simulation:
** Severe ** For PlantLoop=COLLECTOR LOOP DEMAND SIDE CONNECTORS
** ~~~ ** ...Item=COLLECTOR LOOP DEMAND SIDE MIXER, Type=CONNECTOR:MIXER was not matched.
** ~~~ ** The BranchList for this Connector:Mixer does not match the BranchList for its corresponding Connector:Splitter.
** Severe ** For PlantLoop=COLLECTOR LOOP DEMAND SIDE CONNECTORS
** ~~~ ** ...Item=COLLECTOR LOOP DEMAND SIDE SPLITTER, Type=CONNECTOR:SPLITTER was not matched.
** ~~~ ** The BranchList for this Connector:Splitter does not match the BranchList for its corresponding Connector:Mixer.
** Severe ** For PlantLoop=COLLECTOR LOOP SUPPLY SIDE CONNECTORS
** ~~~ ** ...Item=COLLECTOR LOOP SUPPLY SIDE MIXER, Type=CONNECTOR:MIXER was not matched.
** ~~~ ** The BranchList for this Connector:Mixer does not match the BranchList for its corresponding Connector:Splitter.
** Severe ** For PlantLoop=COLLECTOR LOOP SUPPLY SIDE CONNECTORS
** ~~~ ** ...Item=COLLECTOR LOOP SUPPLY SIDE SPLITTER, Type=CONNECTOR:SPLITTER was not matched.
** ~~~ ** The BranchList for this Connector:Splitter does not match the BranchList for its corresponding Connector:Mixer.
** Severe ** For PlantLoop=REGEN HOT WATER LOOP SUPPLY SIDE CONNECTORS
** ~~~ ** ...Item=REGEN HOT WATER LOOP SUPPLY SIDE MIXER, Type=CONNECTOR:MIXER was not matched.
** ~~~ ** The BranchList for this Connector:Mixer does not match the BranchList for its corresponding Connector:Splitter.
** Severe ** For PlantLoop=REGEN HOT WATER LOOP SUPPLY SIDE CONNECTORS
** ~~~ ** ...Item=REGEN HOT WATER LOOP SUPPLY SIDE SPLITTER, Type=CONNECTOR:SPLITTER was no
__._,_.___
View attachments on the web
Posted by: Bruce Ma <brucema1988@xxxxxxxxxxxx>
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
Attachment not found:
D:\Eudora\Attach\Type B-SDAC-HBA-2.idf
Attachment not found:
D:\Eudora\Attach\SystemDiagram.JPG
Attachment not found:
D:\Eudora\Attach\PlantLoopDiagram.JPG