Jean - 
Thanks for the reply!  The model is for LEED, so any amount of unmet hours over 300 is non-compliant for the baseline.  I'm at about 700 for the zone i'm looking at.  
The settings are a .2 deg C thermostat tolerance and a 3600 second cycle time for the availabilitymanager:nightcycle object. If it ultimately cycles off and lets the zone temp creep up before re-engaging, how do you keep the unmet load hours down for LEED? 
I'm modeling the Appendix G System 7.  I think that the HVACtemplate:VAV:System object can also do the type of nightcycle control that you described, although the fan mode is read from the overall availability schedule, and not the supply fan operating mode schedule.
Cheers,