To repeat my answer from earlier:
At 12:19 PM 12/27/2014, Linda Lawrie linda@xxxxxxxxxxxxxx [EnergyPlus_Support] wrote:
This says the fluid properties for Glycol Specific heat have reached outside the range of the inputs for those same properties.

I believe if you look at some of the example PV files -- you will see the same messages.

And to expand:
In your submission to the helpdesk and earlier here, you mentioned/showed you were using V7.0 -- that's why I referenced later versions.

In your current message, you see that it is referring to WATER as the fluid.  Water freezes at 0C and boils at 100C -- so that is why these messages appear. (too cold, too hot) If you used a different fluid (ethylene or propolene glycol, for example) you might not see these messages.

You can ignore these messages or change the fluid to a different glycol or enter your own fluid properties.

At 10:38 PM 12/28/2014, Zahra Balador zbalador@xxxxxxxxx [EnergyPlus_Support] wrote:


The example file have this problem too?
I also have this warning

Sent from Yahoo Mail on Android


From: Ooi Koon Beng ooi_kb3@xxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>;
To: EnergyPlus_Support@xxxxxxxxxxxxxxx <energyplus_support@xxxxxxxxxxxxxxx>;
Subject: [EnergyPlus_Support] Re: ep-help
Sent: Mon, Dec 29, 2014 12:59:07 AM

 

Hi Linda,Â
Â
Re your mention of 'later versions', I am using v8.2, the latest, for SolarCollector:FlatPlate. I get
Â
** Warning ** GetSpecificHeatGlycol: Temperature is out of range (too high) for fluid [WATER] specific heat **
   **   ~~~   ** ..Called From:UpdateSolarCollector,Temperature=[132.38], supplied data range=[0.00,125.00]
   **   ~~~   **  Environment=4-8RUN, at Simulation time=04/01 10:20 - 10:30
   ************* Simulation Error Summary *************
 Â
   ************* ===== Recurring Error Summary =====
   ************* The following recurring error messages occurred.
   *************
   *************  ** Warning ** GetSpecificHeatGlycol: Temperature out of range (too high) for fluid [WATER] specific heat **
   *************  **   ~~~   **   This error occurred 2533 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.
   *************  **   ~~~   **   Max=229.809967 {C}  Min=125.014418 {C}Â
Â
Sometimes I also get Density out of range. It would be good if there is some explanation to this. Is it important?
Â
regards
ooi




__._,_.___

Posted by: Linda Lawrie <linda@xxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___