Re: [EnergyPlus_Support] Why different electricity consumption?





Please let me know how I should define a changing set point for the design days.


On Friday, February 13, 2015 11:55 AM, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
Thanks! This is indeed the case.


On Thursday, February 12, 2015 2:48 PM, "Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
the 2nd and 3rd senario both have a setpoint at 5am of 27 that changes in one step to 24. I bet you used the same schedule for the winterdesignday and summerdesignday because your schedule probably used the alldays keyword which therefor included these day types. This deturmines the size of these two equipments as being almost if not identical.

the first scenario uses (also for the designday) a constant 24 deturmining a different equipment size. So you should expect senario 2 and 3 to be very similar and 1 to be different. And that is indeed the case.

Tip: be specific on the setpoint schedule used during the design days to size you equipment. the common way to avoid oversizing is to keep a constant temperature with no steps for sizing days. the other option is to specify an acceptable "pull down" time which deturmines the amount of time the equipment is allowed to take to meet the setpoint after the step change is imposed...typically 0.5 hours for an air system. Otherwize, the equipment is oversized to meet the instantanious peak averaged over the timestep and oversized equipment is inefficient when operating at part load.

2015-02-12 16:13 GMT+01:00 Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 
the three scenarios are as follows
  • Set point 24 hr = 24C
  • Set point (5am-9pm) = 24C; set point (9pm-5am) = 27
  • Set point (5am-2pm; 5pm-9pm) = 24C; set point (2pm-5pm, 9pm-5am) = 27C; 


On Thursday, February 12, 2015 6:48 AM, "'jeannieboef@xxxxxxxxx' jeannieboef@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
What are your setback temperatures for the 24 and 27 senarios...perhaps the step from setback to setpoint has the same amplitude? 

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold

On 11.02.2015, at 21:45, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 
But then why are red and blue values same during the highlighted time if it has to do with autosizing? The green line indicates the scenario when cooling set point is kept at 24C all day, while red and blue lines indicate scenarios when cooling set points are either 24C or 27C.


On Wednesday, February 11, 2015 12:00 PM, "'jeannieboef@xxxxxxxxx' jeannieboef@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
If you autosized the system, then your equipments are not the same size and will perform marginally different (part-load performance).

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold

On 11.02.2015, at 14:31, "Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 
its the same system simulated with different cooling set points, but during the highlighted time in the three sets of simulations the cooling set point is 24C.


On Tuesday, February 10, 2015 11:28 PM, "Rajeev rajeevkamal@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
What are these profiles of? Every system behaves differently and can be within the error range of measurement and operations.

Sent from my iPhone

On Feb 10, 2015, at 10:32 PM, Fakeha Sehar fakeha_s@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 
Inline image

In the attached figure, three electricity consumption profiles are shown.  All profiles during the highlighted time have same set point of 24 deg C, so why the green colored line has slightly lower electricity consumption?
<blob.jpg>













__._,_.___

Posted by: Fakeha Sehar <fakeha_s@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___