[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] OA reset Schedule_ASHRAE 90.12007





It sounds like you reset the coil water temp, yet still require a outlet air temp that is not achievable with those water temps.

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)

i. A.
Jean Marais
b.i.g. bechtold
Tel.   +49 30 6706662-23

On 23.02.2015, at 21:04, "Harshul Singhal harshul263@xxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

Hi

I am trying to assign OA reset schedule (as per ASHRAE 90.1) for HW and CHW loops. Interestingly it gives millions of errors for Water Coil controllers. If I use simple SetpointManager:Scheduled, it doesnt give errors. Can you please look into it and see what's the issue in here? I am also attaching IDF file, snapshot of my OA reset schedules & errors.

ErrorType:

FindRootSimpleController: Controller error for controller = "CONTROLLER WATER COIL 11"
   **   ~~~   **  Environment=RUN PERIOD 1, at Simulation time=03/03 10:00 - 11:00
   **   ~~~   **   Controller function is inconsistent with user specified controller action = "" action
   **   ~~~   **   Actuator will be set to maximum action
   **   ~~~   ** Controller control type=Temperature
   **   ~~~   ** Controller temperature setpoint = 11.19 [C]
   **   ~~~   ** Controller sensed temperature = 13.01 [C]
   **   ~~~   ** Controller actuator mass flow rate set to 7.39 [kg/s]
   **   ~~~   ** Controller actuator temperature = 13.33 [C]

Severe  ** FindRootSimpleController: Previous controller action error continues for controller = CONTROLLER WATER COIL 4
   *************  **   ~~~   **   This error occurred 3746 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.

Thanks!
Regards,

Harshul Singhal



"save world, save trees..!!! print the mail if required very urgently"

<3_02232015_VAV_Eplus.expidf>
<OAreset_ASHRAE90.1.jpg>
<3_02232015_VAV_Eplus.err>


__._,_.___

Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___