RE: [EnergyPlus_Support] Need Clarification About Equipment Sizing





Jean

 

Sizing uses safety factor and then has to resolve heating and cooling air flow rates.  So if I have 1000 cfm heating rate and 400 cfm cooling rate, the cooling size gets a 2.5 x increase.

 

I tested and any report for a zone with multiplier is zone size x multiplier�

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Saturday, March 14, 2015 5:29 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Cc: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Need Clarification About Equipment Sizing

 

 

1) the user Value incl. Safety Factor is used.

2) my understanding is everything in the zone, stays in the zone, incl. zone equipment and report without multiplier. The system level stuff like boiler, etc. get a zone value x multiplier and report the total value in the report.

Mit freundlichen Grüßen- Sent from my iPhone (excuse the brevity)

 

i. A.

Jean Marais

b.i.g. bechtold

Tel.   +49 30 6706662-23


On 13.03.2015, at 21:39, "'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:

 

I have two questions about autosize equipment sizing:

 

If I look at ___Zsz.csv I get a design day size for the zone.  When I look at the .HTML sizing report I get a calculated design load and a larger user design load.  The two design days are the same (within rounding). Is the larger user design (safety factor) what is actually used for the simulation?

 

In either report, when I use a zone multiplier, should I divide the value by the multiplier to get the equipment size for the zone? And the corollary, If I enter equipment sizes for a zone with multiplier, should I multiply my equipment size by the multiplier?

 

Thanks in advance�

>

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER 
     | Engineering of Structures and Building Enclosures

41 Seyon Street, Bldg. 1, Suite 500
Waltham, MA 02453


781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com



__._,_.___

Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___