Re: [EnergyPlus_Support] ERROR message :CalcZoneAirTempSetpoints: Illegal control type for Zone





Ned,

The OP posted his schedule, it seems fine. 1 for winter 2 for summer. Do you see a problem with it that I'm missing?

Edward can you post the full idf?

Cheers,
Julien 



Envoyé de mon iPhone

Le 27 mars 2015 à 14:16, "'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :

 

Actually it should be simple�14 is not a valid number for a control typpe.  You need to fix your schedule value�

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, March 27, 2015 7:00 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] ERROR message :CalcZoneAirTempSetpoints: Illegal control type for Zone

 

 

It's hard to say without having the full IDF to run thru the software.

At 06:31 PM 3/26/2015, edwardvuong510@xxxxxxxxx [EnergyPlus_Support] wrote:

Hi,


I keep getting several severe error messages,

" ** Severe  ** CalcZoneAirTempSetpoints: Illegal control type for Zone=THERMAL ZONE 1, Found value=14, in Schedule=ZONE CONTROL TYPE SCHED "



I checked my schedule,  ZONE CONTROL TYPE SCHED in my IDF and I get this,


Schedule:Compact,
    Zone Control Type Sched, !- Name
    Control Type,            !- Schedule Type Limits Name
    Through: 3/31,           !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00,            !- Field 3
    1,                       !- Field 4
    Through: 9/30,           !- Field 5
    For: AllDays,            !- Field 6
    Until: 24:00,            !- Field 7
    2,                       !- Field 8
    Through: 12/31,          !- Field 9
    For: AllDays,            !- Field 10
    Until: 24:00,            !- Field 11
    1;                       !- Field 12
   




I checked the Schedule Type Limits Name, "Control Type", and I get this,


ScheduleTypeLimits,
    Control Type,            !- Name
    0,                       !- Lower Limit Value
    2,                       !- Upper Limit Value
    DISCRETE;                !- Numeric Type





__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___