Re: 2) using the economizer for the HX bypass functunality is a known control. For DOAS (100% ODA), you can force the ODA damper to give 100% ODA in the controller:outdoorair object. I've used this combination on most of my projects. I think it is possible to place a temperature setpoint on the outlet of the HX with a setpoint manager such as setpointmanager:outdoorairreset, so that the HX modulates (rotates faster or slower or uses the bypass damper) to meet this temperature setpoint. A setpoint manager can assign its setpoint to many nodes simultaneously. I think I usually use the same setpoint assigned to that after my heating coil (which is usually after my cooling coil). Both my coils are assigned setpoints that vary from a minimum to a maximum dependant on the total load (multizone). I hope that helps. Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23 On 17.04.2015, at 10:31, "pedromarques.be@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |