[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Temperature (low) out of bounds ERROR





Notice that "small" internal heat gain of >200 W/m2. That is far too large and is probably an input error in your lighting or Equipment object.
You should correct that and see if the simulation works better.

On Sun, May 17, 2015 at 4:32 PM, dhaka.hiteshwari@xxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hey

I am working on an Energyplus model. I am stuck with this severe error and i don't know how to rectify.


Severe  ** Temperature (low) out of bounds [-111.35] for zone="ZONE 2", for surface="SW2WALL"

   **   ~~~   **  During Warmup & Sizing, Environment=HYDERABAD ANN CLG .4% CONDNS DB=>MWB, at Simulation time=05/21 15:40 - 15:42

   **   ~~~   ** Zone="ZONE 2", Diagnostic Details:

   **   ~~~   ** ...Internal Heat Gain [211.473] W/m2

   **   ~~~   ** ...Infiltration/Ventilation [0.000] m3/s

   **   ~~~   ** ...Mixing/Cross Mixing [0.000] m3/s

   **   ~~~   ** ...Zone is part of HVAC controlled system.


Both from other sources and also from .err file, the reason why this error is coming is 


 A temperature out of bounds problem can be caused by several things. The user should check:

   ************* ..1) the weather environment (including the horizontal IR from sky)

   ************* ..2) the level of internal gains with respect to the zone

   ************* ..3) the thermal properties of their materials.  And other things.

   ************* ..A common cause is a building with no or little thermal mass - all materials with Material:NoMass definitions.


I have checked everything. Materials, geometry, I can internal Gains everything is alright.

Please if anybody knows what exactly to do. What should I change or What should I look in?

Thank you

 




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

The truth is still the truth, even if nobody believes it.  A lie is still a lie, even if everyone believes it.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___