Air flow to individual zones is handled by the AirTerminal:SingleDuct:Uncontrolled object.  Each zone that is part of the air loop will have one of these when air is supplied to the zone from that air loop.
Zones which have extract, but no supply can be handled with a ZoneCrossMixing object.

On Tue, Jun 9, 2015 at 5:33 AM, m.waseemahmad@xxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Thanks, these are good ideas BUT what if the AHU is supplying fresh air to more than one zones and also if some of the zones have only extract grills instead of having both supply and extract grills (e.g. in cleaner's room)?

Do I have to model grills and volume controlled dampers? Do I have to model in detail the mass flow rate going into each branch of the duct/room? Please see attached the configuration of one the AHU.

Thanks




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Studies show that four out of every three people have a hard time with math.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___