It would be rather unusual to require two outdoor units for a single zone, unless the zone was very large.  The VRF objects in E+ are zone-based, so it seems that you could model both in the same zone as long as your ZoneEquipment definitions are proper.
I have not tried that, so I'm not sure if it will work from experience. 

On Wed, Jun 24, 2015 at 12:24 PM, m.waseemahmad@xxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi,,

I am currently modeling a VRF system that serves one thermal zone. The brief document that I have states that the zone is served by two outdoor VRF units. I was wondering is there a way to model this? Do i have to add up their cooling/heating capacities and input power or there is some other way around it?

Also, it does mention that the zone also has two indoor units. This could also means that each outdoor unit is connected to each indoor unit. Is it common practice to have two VRFs serving one zone?

Thanks





--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Studies show that four out of every three people have a hard time with math.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___