Waseem,
I have not seen curves with this discontinuity. It seems that you can use the normal low / high / boundary curves; in this case the boundary curve will be a vertical line.
I would test the results by reporting cooling capacity at each timestep and see whether you get correct results, especially at the boundary condition.
Let us know what you find, please.


On Fri, Jul 3, 2015 at 10:48 AM, m.waseemahmad@xxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi Richard and Jim, 

Thanks for your answers. I have another question regarding a same kind of system. What if there is discontinuity (a vertical straight small line) in Manufacturer's actual performance data, please find attached performance curves. The Y-axis is capacity correction factors, which is same as ratio of cooling/heating capacity, right? 

How to make curves in this case as it is different that we normally get for VRF system? Also, this values are at rated frequency, will that make any difference?

P.S. This is a split heat pump system. 

Thanks




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Studies show that four out of every three people have a hard time with math.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___