Re: [EnergyPlus_Support] 100% Fresh Air





A simple way is to build a normal air loop with mixing box, then set the "minimum outdoor air flow rate" in Controller:outdoorair to the equivalent of 100%.

You can also create a schedule for "minimum fraction of outdoor air schedule name" in Controller:outdoorair which has a constant value =1.0

On Sat, Aug 22, 2015 at 4:31 AM, a.aelhefni@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

hi guys ,

How can I represent a 100% fresh outdoor air in energyplus ?

Is it possible to build a system like that with energyplus that has no return air ?

thanks




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Life is not easy.  Itâ??s never been easy. Expecting it to be easy is not a healthy attitude.
Relax. Refresh. Regroup. Carry on.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___