Nice description. One missing puzzle piece. The program also calculates the coil entering air conditions, including outdoor air. This air condition, plus those specified by the user as supply conditions, along with the calculated peak zone air flow rate, are used to size the coil. Additionally, the DX coil uses the CapFT curve to correct the coil size for the off-design entering air condition (adjusts back to 80/67 entering air). On 9/3/2015 2:57 AM, Jean Marais
jeannieboef@xxxxxxxxx [EnergyPlus_Support] wrote:
-- Richard Raustad Florida Solar Energy Center 1679 Clearlake Road Cocoa, FL 32922 Ph: (321)638-1454 http://www.fsec.ucf.edu/en/ Program Director Electric Vehicle Transportation Center http://evtc.fsec.ucf.edu/ __._,_.___ Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |