Re: [EnergyPlus_Support] energy wheels





I think that you are limited to defining an air-air heat exchanger with xx% efficiency for sensible and latent heat exchange.  The efficiency can be defined as different values for several part load conditions.

On Mon, Sep 21, 2015 at 10:25 AM, alyelhefni@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi all ,
I want to use the following components in my energyplus simulation :
ENTHALPY WHEEL
SENSIBLE WHEEL
DESICCANT WHEEL
I also should define the material of coating , as far as I know , the 3 differ in coating only and therefore defining effectiveness on energyplus wont point which wheel type Im using .
So how can I define each type specifically and how can I define coating material ?
I also have their equations , can i define a block on energyplus and use it instead ?




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

â???happiness is the joy produced in us by truth. To be truly happy means coming to know how things really are, experiencing ?reality in its ultimate rootâ??¦
What matters more to oneâ??s happiness than getting more freedom and power is the end toward which we order whatever freedom and power we have. Unless we order ourselves to the truth, more freedom and more power will bring only more unhappiness, examples of which abound.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___