I have created a very simple model, because I want to understand how I can model a VAV system where the ventilation rates are lower during the weekends and the air system operates always with 100% outdoor air (I don't want any recirculation).

During the occupation hours I want to have 1,00m3/s during week days and 0,10m3/s during the weekends, therefore I have imposed the following control:


Controller:OutdoorAir,

Air Loop AHU Outdoor Air Controller, !- Name

Air Loop AHU Relief Air Outlet, !- Relief Air Outlet Node Name

Air Loop AHU Extract Fan Air Outlet Node, !- Return Air Node Name

Air Loop AHU Mixed Air Outlet, !- Mixed Air Node Name

Air Loop AHU Outdoor Air Inlet, !- Actuator Node Name

1, !- Minimum Outdoor Air Flow Rate {m3/s}

1, !- Maximum Outdoor Air Flow Rate {m3/s}

NoEconomizer, !- Economizer Control Type

ModulateFlow, !- Economizer Control Action Type

, !- Economizer Maximum Limit Dry-Bulb Temperature {C}

, !- Economizer Maximum Limit Enthalpy {J/kg}

, !- Economizer Maximum Limit Dewpoint Temperature {C}

, !- Electronic Enthalpy Limit Curve Name

, !- Economizer Minimum Limit Dry-Bulb Temperature {C}

NoLockout, !- Lockout Type

FixedMinimum, !- Minimum Limit Type

mechvent pterra, !- Minimum Outdoor Air Schedule Name

On, !- Minimum Fraction of Outdoor Air Schedule Name

mechvent pterra, !- Maximum Fraction of Outdoor Air Schedule Name

, !- Mechanical Ventilation Controller Name

, !- Time of Day Economizer Control Schedule Name

No, !- High Humidity Control

, !- Humidistat Control Zone Name

1, !- High Humidity Outdoor Air Flow Ratio

Yes, !- Control High Indoor Humidity Based on Outdoor Humidity Ratio

BypassWhenWithinEconomizerLimits; !- Heat Recovery Bypass Control Type


where the schedule is


Schedule:Compact,

mechvent pterra, !- Name

Fraction, !- Schedule Type Limits Name

Through: 12/31, !- Field 1

For: Weekdays SummerDesignDay WinterDesignDay, !- Field 2

Until: 08:30, !- Field 3

0, !- Field 4

Until: 18:00, !- Field 5

1, !- Field 6

Until: 24:00, !- Field 7

0, !- Field 8

For: AllOtherDays, !- Field 9

Until: 08:30, !- Field 10

0, !- Field 11

Until: 18:00, !- Field 12

.1, !- Field 13

Until: 24:00, !- Field 14

0; !- Field 15


Since the air flow shall be independent from the cooling load and from the heating load, I have forced the air flow rates in Sizing:System.

As fan I'm using Fan:VariableVolume and as terminal AirTerminal:SingleDuct:Uncontrolled


If I consider the output, the outdoor air flow rate is modulated properly, but there is recirculation (the supplied air flow rate, i.e. OA + recirculated air, is constantly equal to 1m3/s).

I attach the model.

What is wrong?

Best Regards

Francesco




__._,_.___
View attachments on the web

Posted by: fpasserini.tn@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment not found:
D:\Eudora\Attach\VAV1.idf