Re: [EnergyPlus_Support] evaporative cooling





Eduardo,
I have not attempted to do so, but E+ has water usage objects and I suspect that you can set these to monitor the amount of water used by the evap system.

If, instead, you are interested in measuring the sensible cooling energy provided by the evap cooling, you could create a Meter:Custom for Output:Variables like:
  • Zone Air System Sensible Cooling Rate or 
  • Zone Predicted Sensible Load to Setpoint Heat Transfer Rate
Note: I haven't tried the second option either, but it seems that it should work well.

On Wed, Nov 11, 2015 at 10:38 AM, Eduardo Grala da Cunha eduardogralacunha@xxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Dear Jim

I was with the same problem (that is a understanding problem). The problem is that we do not have energy comsumption for the fans, only for heating (elétrica resistence). Where would be the evaporative cooling comsumption for the environmental cooling (fan comsumption)?

With best regards,

Eduardo Cunha
UFPel/Brazil




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

We will forever be crippled if we let emotion or unexamined reactions govern our thoughts and actions. 



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___