|
I’m not sure you have a problem. 12 C supply air is pretty typical for cooling. The energy associated with the volume of 12 C supply air heated and humidified
to the 24 C room conditions should equal the zone solar and infiltration heat gains�. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
hi all , I have a problem that the energy transfer from zone ( cooling ) is very low compared to cooling energy provided by the cooling coil . The enthalpy at the tip of the air distribution unit feeding zone is nearly the same as enthalpy of air exiting the cooling coil . The supplied air is much drier and has temperautre aprox of 12 C while zone should be held at 24 C . How can I solve the problem of zone energy transfer ? __._,_.___ Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |