RE: [EnergyPlus_Support] energy transfer in zone low





I’m not sure you have a problem.  12 C supply air is pretty typical for cooling.  The energy associated with the volume of 12 C supply air heated and humidified to the 24 C room conditions should equal the zone solar and infiltration heat gains�.

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Tuesday, January 05, 2016 11:48 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] energy transfer in zone low

 

 

hi all ,

I have a problem that the energy transfer from zone ( cooling ) is very low compared to cooling energy provided by the cooling coil .

The enthalpy at the tip of the air distribution unit feeding zone is nearly the same as enthalpy of air exiting the cooling coil .

The supplied air is much drier and has temperautre aprox of 12 C while zone should be held at 24 C .

 

How can I solve the problem of zone energy transfer ?



__._,_.___

Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___