Re: [EnergyPlus_Support] Coil on off according to humidity ratio





I use a simple EMS program for turning off DX coils below a specified outdoor temperature.  Something similar may work for you and humidity ratio.

EnergyManagementSystem:Sensor
OutdoorTemp
Environment
Site Outdoor Air Drybulb Temperature


EnergyManagementSystem:Actuator
DXLowLimit1
Sched_LowTempClgOFF
Schedule:Compact
Schedule Value


EnergyManagementSystem:ProgramCallingManager
DXLowLimit Management1
BeginTimestepBeforePredictor
DXCoilControl1


EnergyManagementSystem:Program
DXCoilControl1
IF (OutdoorTemp < 12.8)
SET DXLowLimit1 = 0.0
ELSE
SET DXLowLimit1 = Null
ENDIF


On Thu, Feb 4, 2016 at 8:48 AM, alyelhefni@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I want to make coil available (on) when humidity ratio (w) is above certain value and off if below .

Is there a way the program can decide that automatically without the need to creating an excel schedule file ?




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Fail faster!



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___