Re: [EnergyPlus_Support] No convection losses on the walls when it is raining?





If your weather file has precipitation (some TMY3 files, for example), that could be where you are getting the rain.

You can also choose in the object:
RunPeriod,
  [ snip ]
    NO,                     !- Use Weather File Rain Indicators
   [ snip ]

At 02:03 PM 2/9/2016, joaofranciscopinto@xxxxxxxxx [EnergyPlus_Support] wrote:


I found out that the convection coefficients are set to a very high number when there is rain, causing the problem I mentioned above. What is difficult for me to understand is that these high variations in convection gains only happen with some weather files.

I checked all the flags for rain in my weather file and they are all set for "no rain", so I cannot figure out how to fix this issue.