[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] "Energy Consumption"





Dear Mr. Ademilson Xavier.
Thank you for your great suggestions and it is working. In that case for the Template:Zone:IdealLoadsAir System" in the HVAC Templates Group I input the followings:

HVACTemplate:Thermostat,
    Thermostrat,             !- Name
    Heating-Supply-Air-Temp-Sch,  !- Heating Setpoint Schedule Name
    18,                      !- Constant Heating Setpoint {C}
    Cooling-Supply-Air-Temp-Sch,  !- Cooling Setpoint Schedule Name
    26.7;                    !- Constant Cooling Setpoint {C}


!-   ===========  ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:IDEALLOADSAIRSYSTEM ===========

HVACTemplate:Zone:IdealLoadsAirSystem,
    Z-1,                     !- Zone Name
    Thermostrat,             !- Template Thermostat Name
    Cooling-Supply-Air-Temp-Sch,  !- System Availability Schedule Name
    50,                      !- Maximum Heating Supply Air Temperature {C}
    13,                      !- Minimum Cooling Supply Air Temperature {C}
    0.0156,                  !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
    0.0077,                  !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
    NoLimit,                 !- Heating Limit
    ,                        !- Maximum Heating Air Flow Rate {m3/s}
    ,                        !- Maximum Sensible Heating Capacity {W}
    NoLimit,                 !- Cooling Limit
    ,                        !- Maximum Cooling Air Flow Rate {m3/s}
    autosize,                !- Maximum Total Cooling Capacity {W}
    Heating-Supply-Air-Temp-Sch,  !- Heating Availability Schedule Name
    Cooling-Supply-Air-Temp-Sch,  !- Cooling Availability Schedule Name
    Humidistat,              !- Dehumidification Control Type
    0.7,                     !- Cooling Sensible Heat Ratio {dimensionless}
    60,                      !- Dehumidification Setpoint {percent}
    Humidistat,              !- Humidification Control Type
    60,                      !- Humidification Setpoint {percent}
    None,                    !- Outdoor Air Method
    0.00944,                 !- Outdoor Air Flow Rate per Person {m3/s}
    ,                        !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
    ,                        !- Outdoor Air Flow Rate per Zone {m3/s}
    ,                        !- Design Specification Outdoor Air Object Name
    None,                    !- Demand Controlled Ventilation Type
    NoEconomizer,            !- Outdoor Air Economizer Type
    None,                    !- Heat Recovery Type
    0.7,                     !- Sensible Heat Recovery Effectiveness {dimensionless}
    0.65;                    !- Latent Heat Recovery Effectiveness {dimensionless}

Now for the Facility Total HVAC Electric Demand Power (output), in that case how I can include Fan/coil efficiency with this IdealLoadsAir System (from where)? Thank you so much. 
Regards, 
Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.



On Tuesday, April 12, 2016 8:40 PM, "ademilson xavier ademilsonxavier@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
Hello Mr Chowdhury;

Regarding Energy Consumption I think you could try some reports as "EnergyMeters" or "EndUseEnergyConsumptionElectricityMonthly" by Output:Table - Group and/or "Facility Total HVAC Electric Demand Power" by Output:Variable - Group. However the COP values and Efficiencyof Fan need to be set.

Regarding to RH analysis you can use a "Maximun Heating/Cooling Supply Air Humidity Ratio" into HVAC "Template:Zone:IdealLoadsAir System" in the HVAC Templates Group.

My best regards;

Ademilson Xavier.

(51) 8575 0797


De: "Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Para: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Enviadas: Terça-feira, 12 de Abril de 2016 7:39
Assunto: Re: [EnergyPlus_Support] "Energy Consumption"

 
Thank you. Yes I am using DX coil and Fan. But in that case if I want to calculate only cooling energy and Electric Consumption with the template of PTAC load and Thermostat (set point Heating 18C and cooling 26.7 C, RH=65%), I can manage the indoor set point but could not control the RH which I need (65%). Can you suggest?

IDF,HVACTemplate:Thermostat,Thermostrat,Heating-Supply-Air-Temp-Sch,18,Cooling-Supply-Air-Temp-Sch,26.7; 
IDF,HVACTemplate:Zone:PTAC,Z-1,Thermostrat,autosize,autosize,autosize,,,Maximum, .0000025,,,Cooling-Supply-Air-Temp-Sch,FAN_SCH,BlowThrough, .8, 300, .9,SingleSpeedDX,Cooling-Supply-Air-Temp-Sch,autosize,autosize, 3,Electric,Heating-Supply-Air-Temp-Sch,autosize, .8,,,SupplyAirTemperature, 14, 11.11,SupplyAirTemperature, 50, 30,,,None,,autosize;
 
Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.
Assistant Professor, Dept. of Architecture (Study Leave)
Chittagong University of Engineering & Technology Chittagong 4349, Bangladesh
Present Address:
Laboratory of Environmental Ergonomics
(Planning and Performances for Built Environment)
Division of Human Environmental Systems
Graduate School of Engineering
Hokkaido University, N13-W8, Kita-ku, Sapporo 060-8628, JAPAN
Mobile(P): +818096126951
, E-MAIL: sajal_c@xxxxxxxxx


On Tuesday, April 12, 2016 7:23 PM, "Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 
Inthink you will need to add the energy of individual components. E.g., fan + DX coil

On Tuesday, April 12, 2016, Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 
Dear All,
Is there any output variable for the calculation of direct "Energy Consumption" of HVAC system? Or how I can calculate Energy Consumption from EP simulation of HP/Ideal Load/VAV/ VAF etc. Thank you.
 
Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.



--
James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn
Guitar strings are in constant tension against the guitar's neck during their entire life. The tension doesnâ??t discourage the guitarâ??s neck. Rather, it allows beautiful music to be made. May it be so with our lives and their tensions.









__._,_.___

Posted by: Sajal Chowdhury <sajal_c@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___