Hi Chowdhury;Good to now it!To set or analyze the Fan/coil efficiency in the PTAC (HVAC) you can use a Supply Fan Operating Mode Schedule Name Group within fields as Supply Fan Total Efficiency, Supply Fan Delta Pressure or Supply Fan Motor Efficiency.
De: "Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Para: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Enviadas: Terça-feira, 12 de Abril de 2016 9:14
Assunto: Re: [EnergyPlus_Support] "Energy Consumption"
Dear Mr. Ademilson Xavier.Thank you for your great suggestions and it is working. In that case for the Template:Zone:IdealLoadsAir System" in the HVAC Templates Group I input the followings:HVACTemplate:Thermostat,
Thermostrat, !- Name
Heating-Supply-Air-Temp-Sch, !- Heating Setpoint Schedule Name
18, !- Constant Heating Setpoint {C}
Cooling-Supply-Air-Temp-Sch, !- Cooling Setpoint Schedule Name
26.7; !- Constant Cooling Setpoint {C}
!- =========== ALL OBJECTS IN CLASS: HVACTEMPLATE:ZONE:IDEALLOADSAIRSYSTEM ===========
HVACTemplate:Zone:IdealLoadsAirSystem,
Z-1, !- Zone Name
Thermostrat, !- Template Thermostat Name
Cooling-Supply-Air-Temp-Sch, !- System Availability Schedule Name
50, !- Maximum Heating Supply Air Temperature {C}
13, !- Minimum Cooling Supply Air Temperature {C}
0.0156, !- Maximum Heating Supply Air Humidity Ratio {kgWater/kgDryAir}
0.0077, !- Minimum Cooling Supply Air Humidity Ratio {kgWater/kgDryAir}
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {W}
NoLimit, !- Cooling Limit
, !- Maximum Cooling Air Flow Rate {m3/s}
autosize, !- Maximum Total Cooling Capacity {W}
Heating-Supply-Air-Temp-Sch, !- Heating Availability Schedule Name
Cooling-Supply-Air-Temp-Sch, !- Cooling Availability Schedule Name
Humidistat, !- Dehumidification Control Type
0.7, !- Cooling Sensible Heat Ratio {dimensionless}
60, !- Dehumidification Setpoint {percent}
Humidistat, !- Humidification Control Type
60, !- Humidification Setpoint {percent}
None, !- Outdoor Air Method
0.00944, !- Outdoor Air Flow Rate per Person {m3/s}
, !- Outdoor Air Flow Rate per Zone Floor Area {m3/s-m2}
, !- Outdoor Air Flow Rate per Zone {m3/s}
, !- Design Specification Outdoor Air Object Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.7, !- Sensible Heat Recovery Effectiveness {dimensionless}
0.65; !- Latent Heat Recovery Effectiveness {dimensionless}Now for the Facility Total HVAC Electric Demand Power (output), in that case how I can include Fan/coil efficiency with this IdealLoadsAir System (from where)? Thank you so much.Regards,Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.On Tuesday, April 12, 2016 8:40 PM, "ademilson xavier ademilsonxavier@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
Hello Mr Chowdhury;Regarding Energy Consumption I think you could try some reports as "EnergyMeters" or "EndUseEnergyConsumptionElectricityMonthly" by Output:Table - Group and/or "Facility Total HVAC Electric Demand Power" by Output:Variable - Group. However the COP values and Efficiencyof Fan need to be set.Regarding to RH analysis you can use a "Maximun Heating/Cooling Supply Air Humidity Ratio" into HVAC "Template:Zone:IdealLoadsAir System" in the HVAC Templates Group.My best regards;
De: "Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Para: "EnergyPlus_Support@xxxxxxxxxxxxxxx" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Enviadas: Terça-feira, 12 de Abril de 2016 7:39
Assunto: Re: [EnergyPlus_Support] "Energy Consumption"
Thank you. Yes I am using DX coil and Fan. But in that case if I want to calculate only cooling energy and Electric Consumption with the template of PTAC load and Thermostat (set point Heating 18C and cooling 26.7 C, RH=65%), I can manage the indoor set point but could not control the RH which I need (65%). Can you suggest?IDF,HVACTemplate:Thermostat,Thermostrat,Heating-Supply-Air-Temp-Sch,18,Cooling-Supply-Air-Temp-Sch,26.7;IDF,HVACTemplate:Zone:PTAC,Z-1,Thermostrat,autosize,autosize,autosize,,,Maximum, .0000025,,,Cooling-Supply-Air-Temp-Sch,FAN_SCH,BlowThrough, .8, 300, .9,SingleSpeedDX,Cooling-Supply-Air-Temp-Sch,autosize,autosize, 3,Electric,Heating-Supply-Air-Temp-Sch,autosize, .8,,,SupplyAirTemperature, 14, 11.11,SupplyAirTemperature, 50, 30,,,None,,autosize;Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.
Assistant Professor, Dept. of Architecture (Study Leave)
Chittagong University of Engineering & Technology Chittagong 4349, Bangladesh
Present Address:
Laboratory of Environmental Ergonomics
(Planning and Performances for Built Environment)
Division of Human Environmental Systems
Graduate School of Engineering
Hokkaido University, N13-W8, Kita-ku, Sapporo 060-8628, JAPAN
Mobile(P): +818096126951, E-MAIL: sajal_c@xxxxxxxxxOn Tuesday, April 12, 2016 7:23 PM, "Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
Inthink you will need to add the energy of individual components. E.g., fan + DX coil
On Tuesday, April 12, 2016, Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:Dear All,Is there any output variable for the calculation of direct "Energy Consumption" of HVAC system? Or how I can calculate Energy Consumption from EP simulation of HP/Ideal Load/VAV/ VAF etc. Thank you.Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.
--James V Dirkes II, PE, BEMP, LEED AP