I caution that Design Days are by definition atypical conditions with the daily maxima corresponding to either the 0.6% or 1% highest hourly temperatures. Furthermore, the hourly profile described below is extremely generic and applied to all locations and conditions. I don't know how you intend to use the "daily variation sine curve", but if it's to understand the average daily temperatures for each month, I would recommend calculating the average daily max/min from the weather file or even easier from Wikipedia, and then use the ASHRAE Design Day Profile to fill out the 24 hour values. If you want to be more location-specific, you can analyze the weather file to derive the average monthly profiles. Last comment is that the daily profiles are not sine curves. Joe Sent from my iPad On Apr 16, 2016, at 9:20 AM, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ View attachments on the web Posted by: Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |