Re: [EnergyPlus_Support] Cooling Load Calculation





Dear Sajal,

I imagine you're looking at the wrong thing …
In the early part of his "Table.HTML" there is a table with the title "End Uses.” This table is divided into some columns: Electricity [kWh], Natural Gas [kWh] Additional Fuel [kWh] District Cooling [kWh] District Heating [kWh] Water [m3], according to the source of energy used.
If so, just watch the values for "Heating", "Cooling" and "Fans" and convert them to GJ using the ratio 1 [kWh] = 0.0036 x [GJ / h].

Otherwise, based on Input/Output Reference Guide, it appears that your file is set to IDF kWh “ClassList" > "OutputControl: Table: Style". There is a possibility that the data are provided in:
- JtoKWH - Joules converted into kWh (1 / 3,600,000)
- JtoMJ - Joules converted into megajoules (1 / 1,000,000)
- JtoGJ - Joules converted into gigajoules (1 / 1,000,000,000)
- InchPound - convert all annual, monthly, economics and timebins tabular values ​​to common Inch-Pound equivalent
Remember: the current options are limited to just how the energy is being Reported.

God job,
Arq Carlos Krebs
Me Arquitetura e Urbanismo
PROGRAU/FAUrb/UFPEL
LEED® Accredited Professional
Auditor Interno ISO 14.001
Consultor de Eficiência
Energética em Edificações




On Jun 21, 2016, at 7:32 AM, Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


Dear All,
I calculated the following by using ILAS for 1 year.
Report: HVAC Sizing Summary
For: Entire Facility
Zone Cooling


Calculated Design Load [W]User Design Load [W]User Design Load per Area [W/m2]Calculated Design Air Flow [m3/s]User Design Air Flow [m3/s]Design Day NameDate/Time Of PeakThermostat Setpoint Temperature at Peak Load [C]Indoor Temperature at Peak Load [C]Indoor Humidity Ratio at Peak Load [kgWater/kgAir]Outdoor Temperature at Peak Load [C]Outdoor Humidity Ratio at Peak Load [kgWater/kgAir]
PRODUCTION ZONE39246.6139246.6111.682.3372.337SIZINGPERIOD7/26 14:00:000.0026.700.0077030.000.02274

Here, Calculated Design Cooling Load [W]= 39246.61 W .. is this calculation for per second ??? and if I want to convert this to GJ per Hour how can I do this?? Thank you. 

Best Wishes, 
 
Sajal Chowdhury 
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.





__._,_.___

Posted by: Carlos Krebs <clmkrebs@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___