Re: [EnergyPlus_Support] Pool Cover does not work





Jonathan,
Assuming that you mean the "Indoor Pool Evaporative Heat Loss Rate [W]" report variable and that "Cover Evaporation Factor" is not = 0, then your results seem clearly to be incorrect.

I recommend that you send your file to the Help Desk for review.  The swimming pool object is relatively new and may need some refinement.

p.s., It is a sign of a good modeler that he checks the results carefully. Good work!

On Fri, Jun 24, 2016 at 6:52 AM, jduverge1979@xxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi There

Has anyone use the indoor swimming pool ?
I'm trying to simulate an indoor door and work out the effect of pool cover on evaporation rate.
When you look at the variable (indoor Pool evaporation Heat Loss energy) after adjusting the pool cover schedule ( pool cover on from 8pm to 6am and pool cover off from 6am to 8 pm). There is no effect on the indoor Pool evaporation Heat Loss energy variable. You can adjust the pool cover schedule  anyway you want but the indoor Pool evaporation Heat Loss energy variable stay exactly the same.
I think it only works when the pool cover is on 24 hr then the the indoor Pool evaporation Heat Loss energy variable is zero.
I have attached the example swimming pool idf file. Can someone fix that error?

Regards
Jonathan




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

Either I win ? or I learn.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___