Francesco,
Secondary airflow won't help with cooling loads; it's just room air.
If you cannot meet cooling loads, you'll need to change something on the primary / air loop side

On Thu, Jul 28, 2016 at 11:06 AM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I'm facing the same problem as Dante now. The PIU fans turn off only when the primary air flow is above the specified fraction of the maximum (Fan On Flow Fraction), i.e. in the warmest periods of the year.

Do you think I have to use the nightcycle also for the PIU fans?
Paragraph G3.1.2.4 is not clear from this point of view.
Regards




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

There is no such thing as intimacy without surrender. This is true for people and for God. People are more chancy.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___