[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: use thermal cameras to capture occupant heat gain





Hi

I'm not sure how you can use a thermal imaging camera to capture the heat gains from a person because the thermal camera is only a reading of radiative heat and people release heat into the environment also through convection and evaporation and these rates differ dependent on the environmental conditions

you ought to read the engineering reference under the section for Heat gain from people and perhaps re-consider the applicability of your proposal

here is an extract:

The input object People provides a model for internal gains from occupants. Heat is generated in the human body by oxidation at a rate called the metabolic rate (see Thermal Comfort discussion for more details). This heat is dissipated from the body surface and respiratory tract by a combination of radiation, convection, and evaporation. The relative proportions of sensible (radiation plus convection) and latent (evaporation) heat from people is a complex function of the metabolic rate and the environmental conditions. EnergyPlus uses a polynomial function to divide the total metabolic heat gain into sensible and latent portions. That function is based on a fit to data [3] at average adjusted metabolic rates of 350, 400, 450, 500, 750, 850, 1000 and 1450 Btu/h each at temperatures of 70, 75, 78, 80, 82 degrees Fahrenheit. Sensible gains of 0 at 96 F and sensible gains equal to the metabolic rate at 30 F were assumed in order to give reasonable values beyond the reported temperature range.




 


__._,_.___

Posted by: allinson_louis@xxxxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___