[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] Airflownetwork Linkage





I've not modelled AFN with the ducts in that mode. I.e. have always ignored duct leakage and use the other AFN analysis mode. Have you tried Dr Gu? Perhaps they are fully balanced as you suspect. We usually try to design this way in my office for most spaces.

On 24 Aug 2016 6:59 pm, "'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Thanks Jean, but I have a full network of windows and flow paths.  It is just getting the HVAC flow integrated.  The examples all have duplicate nodes back through the air loop and defined leakage in ducts before air actually gets to the zone.  I was hoping to get air into a zone as simply as the exhaust fan can remove air from a zone.  Iâ??m looking at zone pressures and I canâ??t get them to move when the air system comes on, which means they are not modeled or fully balanced.

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files

From: EnergyPlus_Support@yahoogroups.com [mailto:EnergyPlus_Support@yahoogroups.com]
Sent: Wednesday, August 24, 2016 12:05 PM
To: EnergyPlus_Support@yahoogroups.com
Subject: Re: [EnergyPlus_Support] Airflownetwork Linkage

 

 

I think a requirement is at least two cracks abounding to outdoor with a path connection, however complicated, to each other. The HVAC supply then just splices in. You can make the cracks very "tight", but they must be there.

On 24 Aug 2016 5:56 pm, "'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@yahoogroups.com> wrote:

 

I have reviewed an airflownetwork sample file, but I am having some trouble getting a simple supply air flow into the model.  The sample IDF has lots of leakages associated with components which I donâ??t need.  My building supplies air to zones and all air actually returns as makeup air for a kitchen exhaust system.  I figured out how to do an exhaust fan and it will pull the building negative when it runs, but I have not succesed in getting supply air to turn the building positive.  If you are an airflownetwork expert, I would appreciate a little guidance?that hopefully doesnâ???t include having to model every potential leakage point in the systemâ?¦

 

Thanks in advance?

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER 
     | Engineering of Structures and Building Enclosures

41 Seyon Street, Bldg. 1, Suite 500
Waltham, MA 02453

781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___