Assuming that you mean "annual energy use" for "results", that sounds correct.  The DesignDays are used to size equipment, while the weather file is used for annual energy calculations.

I think there should be small differences in energy use when using different DesignDays dues to the varying impact of part load performance curves, but a few degrees difference in the DesignDay won't affect the energy use very much.

On Thu, Aug 25, 2016 at 1:22 PM, ifigeneiat@xxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Dear all, 

I am running a set of simulations in order to compare the difference between the cooling loads for a building with different SummerDesignDay objects according to in-situ measurements for the actual climatic conditions. I have changed the Maximum Dry-Bulb Temperature but there is no difference in the results. 
Any tips?




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

Believers in progress rightly note that in the world of machines, the new model supercedes the old; from this they falsely infer a similar kind of supercession in such things as virtue and wisdom



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___