Francesco,
That should be "close enough" for most energy models. Actual performance, however, is not linear with the number of compressors. In order to know more closely, the manufacturer literature should tell you the actual performance.
Also, a scroll compressor can sometimes unload by operating a fraction of the time. Once again, the manufacturer literature (or a sales representative or the design engineer) should be helpful.
Since you recognize the impact of oversizing and minimum unloading, it is probably worthwhile to investigate more closely.


On Wed, Oct 5, 2016 at 5:53 AM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello, if a chiller has 4 scroll compressors, then the Minimum Unloading Ratio shall be 1/4 (i.e. 0.25), correct?

I want to be sure, because in a model that I'm considering the chiller is oversized and the Minimum Unloading Ratio influences a lot the annual consupmtion.

Regards

Francesco

 




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

?an open mind is not an end in itself but rather is like an open mouth, designed to bite down on something solid and nourishing.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___