[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: [Equest-users] Modelling Non AC building in eQUEST





Sorry,
last message got sent out inadvertently while I was editing it.  The full message is contained below.

-------- Forwarded Message --------
Subject: Re: [Equest-users] Modelling Non AC building in eQUEST
Date: Fri, 17 Feb 2017 14:59:15 -0800
From: Joe Huang via Equest-users <equest-users@xxxxxxxxxxxxxxxxxxxxx>
Reply-To: Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx>
To: equest-users@xxxxxxxxxxxxxxxxxxxxx


I have doubts about how you're doing this.  I used to model non-conditioned buildings in Asia by using the Residential (RESYS) system and setting the Heating and Cooling Setpoint temperatures way below or above the actual room temperature so that they never come on, e.g.,  Heating at 99 and Cooand , which uses a different VENT-TEMP-SCHEDULE for the temperature above which windows are expected to open, e.g., 75 F, PROVIDED that the outdoor air temperature or enthalpy is lower.  To be doubly safe, you can set the Heating and Cooling capacity to very small numbers, like 0.1, etc., although that's immaterial because they would never come on.

I don't see how you can derive unmet hours for an unconditioned space, but you can derive the hours above comfort, e.g., 78 F, and tabulate that.  I used to call them Heating or Cooling Discomfort Hours :-)

Joe

Joe Huang 	
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
http://weather.whiteboxtechnologies.com for simulation-ready weather data
http://www.whiteboxtechnologies.com
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
On 2/14/2017 5:34 AM, Kirti Pabrekar - Patil via Equest-users wrote:
Dear eQuesters, 

I have the following doubt.

1. This is a hostel building. all the rooms are non ac except the wardens cabin and the counselling room. These two rooms have split units. 

2. I have to model this for thermal comfort compliance - so i need to show that there are less unmet hours in the building. 

How do I go about this?

What i thought was as under,

1. I made the entire model and assigned the ac and non ac spaces as per design.
2. I plan to put a system in the non ac rooms, such that the CFM generated due to ceiling fans can be put as Fan Flow Parametres. A 12 hour fan schedule (as per the evening + night time occupancy hours) can be assigned to this. Other than this there will be no input parameter assigned to this system - no COP, no efficiency. Other than this these rooms have to behave as non ac spaces. 

Now my questions,
1. Do you think this is logical way to do?
2. Is there any other way to go about this?
3. If what i have described in point 2 is okay, while i assigning systems what should it be? Like Sum or FNSYS or VAVS etc? Please let me know the specifics

Please give me an insight into this ya. 

Regards
Kirti

Kirti Pabrekar - Patil
M. Arch, LEED GA,
IGBC AP, GRIHA Trainer & Evaluator,

 



Green is a commitment...not a competition


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE@xxxxxxxxxxxxxxx



__._,_.___

Posted by: Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___