|
The water heater will turn on at 52C, the HP turns off at 52C so the water heater tank will heat the water to 55C and the HP will never turn on. WaterHeater:Mixed, Aux HW Loop HP Water Heater Water Heater, !- Name 0.265000, !- Tank Volume {m3} 55C, !- Setpoint Temperature Schedule Name 3, !- Deadband Temperature Difference {deltaC} WaterHeater:HeatPump:PumpedCondenser, 2, !- Dead Band Temperature Difference {deltaC} Switch these so the HP runs most of the time. WaterHeater:Mixed, 52C, !- Setpoint Temperature Schedule Name WaterHeater:HeatPump:PumpedCondenser, Now the HP will heat the
water to 55C and the tank will never turn on since it will wait
for the water temp to drop below 49C. __._,_.___ Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |