[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Coil:Cooling:DX:TwoSpeed and SHR





Ed, feel free to supply me with an input file so I can see where the low speed SHR as a problem with RH > 100%. I have just been making changes in that area and want all coil types to behave well.
rraustad@xxxxxxxxxxxx

On 6/30/2017 3:17 PM, 'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support] wrote:

I am modeling an existing building with several roof top VAV systems.  I have system model numbers so I did not autosize any of the Coil:Cooling:DX:TwoSpeed system.  The SHR inputs for the model and error messages running the model make no sense to me:

 

Manufacturer data says SHR at low speed is much lower than at high speed (makes perfect sense to me), but E+ complains if the high speed and low speed SHR differ too much.

 

Using manufacturer data to calculate SHR inputs results in psychrometric calculation errors about RH exceeding 100%.  While the error message would suggest that more latent cooling is needed (lower SHR) the actual fix is to increase the SHR (less latent cooling).

 

So my model runs now runs without complaints with high speed SHR = low speed SHR = 0.77, not close to the manufacturer data. I would appreciate it if anyone could explain this E+ logic to me this.    

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER 
     | Engineering of Structures and Building Enclosures

41 Seyon Street, Building 1, Suite 500
Waltham, MA 02453

781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files


-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/

Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/


__._,_.___

Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___