You will want to use at least one winter and one summer design days. This answer should be of interest: https://unmethours.com/question/16698/which-cooling-design-day-is-most-common-for-sizing-rooftop-units/ I might add that ashrae appendix G specifies 3 design days that you must use (90.1-2010 says from memory something like 99.6% condns DB (winter), and for summer the .4% DB=>MWB and .4% WB=>MDB) , don’t quite me on this and double check). �� Sent from a mobile device, please excuse the brevity.Julien Marrec, EBCP, BPI MFBA Direct: +33 6 95 14 42 13 Le 20 févr. 2018 à 22:19, my_sunny_night@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien Marrec <julien.marrec@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |