|
Put them in series on the same supply branch of the shw use loop, the stratified tank before the instantaneous one. But more importantly, set your plant loop demand calculation scheme to SequantialLoad and use a plant equipment operation heating load with the stratified tank first in the priority range. �� Sent from a mobile device, please excuse the brevity.Julien Marrec, EBCP, BPI MFBA Direct: +33 6 95 14 42 13 Le 28 juin 2018 à 04:01, costa.civil@xxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien Marrec <julien.marrec@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |