[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Peak heating load vs total energy use





With which output variable, I can check whether additional outdoor air used for ventilation in Case 1 compared to Case 2?

Another thing, all the assumptions for Case 1 and 2 are exactly the same for HVAC sizing using design day. But the design coil load for heating coil water of AHU is lower for Case 2.

Any help would be appreciated.




---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <jim@...> wrote :

As you say, All of the lights and other electric equipment offset the need for heating, so the heating must operate more in Case 2 (when they are OFF).
Iâ??m wondering if the higher peak heating for Case 1 is due to additional outdoor air used for ventilation?


On Wed, Aug 29, 2018 at 9:01 PM my_sunny_night@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hello All,
I have two identical case studies with identical assumptions for everything. I just set people, lights, and electric equipment loads to zero. Let us call this case as Case #2. For Case #1, I used default people, lights, and electric equipment assumptions.
Annual total heating energy use is higher in Case #2 than Case #1, which makes sense.
But, peak heating load in Case #2 is lower than Case #1.
Why peak load of Case #2 is lower than Case #1 while total heating energy use of Case #2 is higher than Case #1?
Thanks for your help.


--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, Grand Rapids, MI 49504

(alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@...

Website l  LinkedIn

Coffee conversation:

You are hereby authorized to make two big mistakes each year, otherwise you will never learn anything.



__._,_.___

Posted by: my_sunny_night@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___