|
Christopher,
For some reason, E+ has always assumed a fixed pump mechanical efficiency of 78% - it's not editable. I agree that it's abnormally high!
For the purposes of an energy model, the pump efficiency doesn't matter IF.... you align flow rate, 78% and the pump head so that the actual
brake horsepower/ kw results. That's what I'm doing with the little spreadsheet calculation. (The pump head used in that calc will NOT normally be what is shown on mechanical drawings when following this approach.)
Alternatively, I think you could specify the Design Power Consumption. As it happens, I have not tested that field, so I can't tell you much about it.
James V Dirkes II, PE, BEMP, BCxP
Team Lead - Building Performance
Foresight Management
616 450 8653
Coffee Conversation:
The first difficulty in the way of the intellect’s functioning well is that it hates to function at all, at any rate beyond the point where functioning begins to require effort. The result is that when any matter arises which is properly the job of the intellect, then either nothing gets done at all, or else the imagination leaps in and does it instead. There is nothing to be done with the intellect until imagination has been put firmly in its place. From: Jones, Christopher <Christopher.r.Jones@xxxxxxx>
Sent: Friday, March 8, 2019 8:41 AM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Cc: Jim Dirkes Subject: RE: [EnergyPlus_Support] HVAC pump with 11 W/gpm Jim, I rarely see a pump shop drawing showing an efficiency as high as 78%. Can one edit the proposed model .idf to use the pump efficiency shown on the shop drawings?
Christopher R Jones, P.Eng. T+ 1 416-644-0252
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
....slightly corrected version
James V Dirkes II, PE, BEMP, BCxP Team Lead - Building Performance Foresight Management 616 450 8653
Coffee Conversation: The first difficulty in the way of the intellect’s functioning well is that it hates to function at all, at any rate beyond the point where functioning begins to require effort. The result is that when any matter arises which is properly the job of the intellect, then either nothing gets done at all, or else the imagination leaps in and does it instead. There is nothing to be done with the intellect until imagination has been put firmly in its place. From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of Jim Dirkes Jim@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Dante, Try the attached calculator, adjusting the "W/gpm" value to 11
James V Dirkes II, PE, BEMP, BCxP Team Lead - Building Performance Foresight Management 616 450 8653
Coffee Conversation: The first difficulty in the way of the intellect’s functioning well is that it hates to function at all, at any rate beyond the point where functioning begins to require effort. The result is that when any matter arises which is properly the job of the intellect, then either nothing gets done at all, or else the imagination leaps in and does it instead. There is nothing to be done with the intellect until imagination has been put firmly in its place. From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of Dante Andres Garcia andresdagm@xxxxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx>
Hello,
I have a general question redarging how to design HVAC pump with 11 W/gpm per primary and secondary loops in evaporator.
Please advise how a design can achieve that target. Most design that I have seen exceeds that limits becasuse it does not consider head.
Regards,
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited.. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance@xxxxxxx so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages. AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap@xxxxxxx afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux. -LAEmHhHzdJzBlTWfa4Hgs7pbKl __._,_.___ Posted by: Jim Dirkes <Jim@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00639.jpg
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00733.jpg
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00823.jpg