[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Is it possible to model in EnergyPlus window ventilation triggered by the history of A/C operations the previous X number of days? [1 Attachment]





Joe,

You'll find in attachment a file that shows the gist. I took the E+ Example file WindACAuto.idf and added a simple EMS program to compute the @TrendSum over 384 timesteps = 4 days (at 4 timesteps/hours).

The interesting bit is right at the end.

Hope that helps,
Julien

--
Julien Marrec, EBCP, BPI MFBA
Owner at EffiBEM
T: +33 6 95 14 42 13

LinkedIn (en) | (fr) :


Le dim. 9 juin 2019 à 23:42, Julien Marrec <julien.marrec@xxxxxxxxx> a écrit :
Hi  Joe,

I am unaware of something built-in but it's certainly possible via EMS.
You'd use a trend variable on an ems sensor like "cooling power W" or On/Off status (whichever variable on your specific cooling object that will serve as a proxy for cooling operation).
In your EMS program you can do a @Sum (or @max...) on your trend variable for the past N timesteps and check if > 0, meaning the AC would have been on during that time.

Hope that helps,
Juliem

--
Sent from a mobile device, please excuse the brevity.

Julien Marrec, EBCP, BPI MFBA
Owner

Direct: +33 6 95 14 42 13
Website: www.effibem.com
LinkedIn (en) | (fr)
On Jun 9, 2019, at 12:08, "Joe Huang YJHuang@xxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support]" <energyplus_support@xxxxxxxxxxxxxxx> wrote:
 

My apologies if my question in the subject line seems unclear. I've been having
difficulties getting good correspondence in residential runs done with DOE-2.1E to doing
them with EnergyPlus, with EnergyPlus showing more than twice the Heating Energy as shown
by DOE-2.1E.  By process of elimination, I've narrowed down the discrepancy to how natural
ventilation through windows is being modeled. These runs are  in California climates where
overcooling by natural ventilation during the day can substantially increase heating
energy at night during the swing season, leading to the 2X increase over  the entire year.

The natural ventilation model in DOE-2 has a feature that checks whether  the AC had been
on for the previous X number of days.  If so, the program then knows that it's the cooling
season, and will then permit window ventilation based on either temperature or enthalpy
difference between the indoor and the outdoor.   If the check finds there was no cooling
the previous X number of days, it then knows it's not in the cooling season and window
ventilation is not permitted. For those who are curious, the actual BDL inputs are as follows:

 VTSCH     SCHEDULE  $Vent schedule based on previous 4 days load
                    THRU MAY 14 (ALL) (1,24) (-4)
                    THRU SEP 30 (ALL) (1,24) (-4)
                    THRU DEC 31 (ALL) (1,24) (-4) ..
VOPSCH    SCHEDULE  $Vent operation schedule
                    THRU DEC 31 (ALL) (1,24) (VTYPE) ..    (where VTYPE =1 for
temperature difference, -1 for enthalpy difference, 0 for no ventilation)
WINDOPER  SCHEDULE  $No window operation between 11 p.m. and 6 a.m.
                   THRU DEC 31 (ALL) (1,6)  (0.0)
                                        (7,23) (1.0)
                                      (24)   (0.0)  ..

I've looked into my EnergyPlus idf and found this:

  Controller:OutdoorAir,
    SYS OA Controller,       !- Name
    SYS Relief Air Outlet,   !- Relief Air Outlet Node Name
    SYS Air Loop Inlet,      !- Return Air Node Name
    SYS Mixed Air Outlet,    !- Mixed Air Node Name
    SYS Outside Air Inlet,   !- Actuator Node Name
    autosize,                !- Minimum Outdoor Air Flow Rate {m3/s}
    autosize,                !- Maximum Outdoor Air Flow Rate {m3/s}
    DifferentialDryBulb,     !- Economizer Control Type
    ModulateFlow,            !- Economizer Control Action Type
    ,                        !- Economizer Maximum Limit Dry-Bulb Temperature {C}
    ,                        !- Economizer Maximum Limit Enthalpy {J/kg}
    ,                        !- Economizer Maximum Limit Dewpoint Temperature {C}
    ,                        !- Electronic Enthalpy Limit Curve Name
    ,                        !- Economizer Minimum Limit Dry-Bulb Temperature {C}
    LockoutWithCompressor,   !- Lockout Type
    FixedMinimum;            !- Minimum Limit Type

which seems not to have such a load-based toggle.   Is there another Residential or Window
Ventilation Object that I should use?  Or is this something that can be programmed using
EMS? I've sorry if I'm asking a well-known question, but I have simply not followed the
development of EnergyPlus for the past 15 years.

Any advice or suggestions would be appreciated.

Joe



__._,_.___
View attachments on the web

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment not found:
D:\Eudora\Attach\WindACAuto_Mod.idf