[Equest-users] Chiller curves
Robby Oylear
robbyo at rushingco.com
Mon Dec 8 07:49:46 PST 2008
The short answer would be no and no. I'm not aware of any curve tools or
libraries and in my experience if you want to use a custom chiller curve
you'll have to build it yourself, with close work with the manufacturer.
To create custom chiller curves you need to have data for the capacity and
efficiency as a function of condenser water supply and chilled water
supply temperatures as well as the kW power draw as a function of part
load and LIFT conditions (Condenser Water Supply Temp - CHW Supply Temp).
This is all in regards to a variable-speed centrifugal water cooled
chiller, I'm not sure how different this would be for an air-cooled
chiller as I haven't tried to use custom data for one yet.
I've attached a PDF of a sample of the data I had to collect from the
manufacturer in order to create a set of custom chiller curves.
Essentially I had to specify the conditions that I wanted efficiency and
capacity numbers for and then the manufacturer was able to use his
selection program to determine the numbers for me.
Hope this helps,
Robby Oylear, LEEDR AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www. <http://www.rushingco.com/> rushingco.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vikram
Sami
Sent: Monday, December 08, 2008 7:35 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chiller curves
Hi,
Is there a chiller curve tool/library out there for specific chillers in
eQUEST? Also - can you create a curve with just the kW/ton and the NPLV?
What are the inputs I need to create a custom chiller curve?
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design . Technological Expertise . Exceptional Service
Please visit our new website | <file:///\\www.lordaecksargent.com\>
www.lordaecksargent.com
P Think GREEN before you print.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081208/7cb2824c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Example Chiller Curve Info.pdf
Type: application/pdf
Size: 15005 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081208/7cb2824c/attachment-0001.pdf>
More information about the Equest-users
mailing list