Report SS-R gives the number of hours the fans are in each part load range.
Generally, with heat pumps, the minimum fan ratio is 1, which means that the
heat pump fans cycle on (100%), then off (0%).  So the report is correct.
If you have variable speed fans for this system, you need to change your
input parameters to allow the fans to cycle at less than 100%.
--
Karen
On Tue, Jul 8, 2008 at 11:00 AM, Alison Staudinger <astaudinger at jdrm.com>
wrote:
>  I'm stumped...
>
>
>
> I let eQuest select the size of my heat pumps, but when I look at the SS-R
> report to see my unmet hours and part load performance every heat pump is
> operating at maximum capacity.  Not a single unit has any part load
> performance.  I would think this could happen if I selected the size of the
> units, but if the program is sizing it, wouldn't it select a unit that is
> large enough to meet capacity which would have to result in some part load
> performance?  There are some units that have many unmet hours (typically
> heating) and others that have no unmet hours.  Both cases have no part load
> hours.  Any input would be appreciated.
>
>
>
> Thanks!
>
>
>
> *Alison Staudinger P.E., LEED AP*
>
> JDRM Engineering
>
> 5604 N. Main St.
>
> Sylvania, OH  43560
>
> (419) 824-2400
>
>
>
> --| Any project file attachments should be sent to files at jdrm.com
>
> --| This mail and all information contained herein is the property
>
> --| of JDRM Engineering, Inc. for use by the intended recipient only !
>
> --| Copyright (c) 2008 JDRM Eng, Inc. All Rights Reserved.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080708/1ab164f7/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list