I had the same warning yesterday and although I cannot explain why the
warning went away, I can tell you what I did and if you're lucky maybe
it will apply for your case as well.  I had 'Packaged Single Zone'
specified for my System Type and 'Plenum' for the Return Air Path of the
system parameters and obviously under my plenum zone I had the Zone Type
as 'Plenum'.  For this isolated space it wasn't actually a plenum (the
remaining 98% of the building is a VAV RA plenum system) so I changed
the system to a 'Direct' Return Air Path and the Plenum Zone to an
'Unconditioned' Zone Type.  After doing that my warning went away.  I
don't know why but thought I would share it anyhow.  Good luck! 
 
Alison Staudinger P.E., LEED AP
JDRM Engineering
5604 N. Main St.
Sylvania, OH  43560
(419) 824-2400
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Frymire, Nathan
Sent: Wednesday, July 16, 2008 10:45 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest Warning
 
Hello-
 
First time posting and glad I found this resource.  This is a tricky
software to learn/utilize on projects.
 
I'm modeling a small office building that we'd like to certify LEED
Silver.  Detailed output is giving me the following message for each
zone:
 
**WARNING***************************************************************
*******
             Zone: EL2 South Perim Zn (G.S6)        could not
successfully
             allocate all equipment energy to the 5-minute bins
             because of an equipment overload.  The peak load
             used in ECONOMICS will not include the fraction due
             to the overload, but the PLANT reports will.
             Mon/Day/Hour: 12 21  8  Energy:   1.9  Unallocated: 0.250
 
Does anyone have an idea what this might be or how to correct it?  It
must have something to do with a control at the zone level.  Any
assistance would be appreciated.  Thanks.
 
 
Nathan R. Frymire, LEED(r) A.P.                        
Mechanical Engineer
Burns & McDonnell
9400 Ward Parkway
Kansas City, MO 64114
 
Phone:  816-822-3900 ext 8513
Fax:  816-822-3423
 
         
www.burnsmcd.com <http://www.burnsmcd.com> 
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080717/72ea3736/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 3181 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080717/72ea3736/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1418 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080717/72ea3736/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list