[Equest-users] Exterior Light Levels
    Alison Staudinger 
    astaudinger at jdrm.com
       
    Fri Jul 18 05:58:31 PDT 2008
    
    
  
Another way to rotate the building is to create a parametric run.  Got
to Tools, Create Parametric Run, I name the run 90 deg. Rotation (and
then 180 deg. For the next and finally 270 deg.).  Run all the runs on
the baseline because you don't want the energy differences compounded.
Next Create Parametric Component - The component type should be
"Building Parameters".   Under Data Modifications have the Category
"build parameters", Keyword "Azimuth", value "90" (then 180, then 270),
units "deg".  This will give you all four orientations 90.1 appendix G
is looking for.
 
Alison Staudinger P.E., LEED AP
JDRM Engineering
5604 N. Main St.
Sylvania, OH  43560
(419) 824-2400
 
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of James
Chong
Sent: Thursday, July 17, 2008 5:58 PM
To: Frymire, Nathan; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Exterior Light Levels
 
To modify exterior light levels, in Air-Side HVAC, look into your
Electric Meter (EM1) properties and select the last tab "Direct Loads".
You can modify the exterior direct load and the schedule there.
 
To rotate the building, in Building Shell, select Building Data
Properties and you can rotate the building by changing the Azimuth
field.
 
 
James Chong 
Student Engineer - Mechanical 
 
MCW Custom Energy Solutions Ltd. <http://www.mcw.com> 
600-156 Front Street West 
Toronto, ON M5J 2L6 
Phone 416-598-2920 
Fax 416-598-5394 
 
This e-mail may be privileged and confidential. Any unauthorized use is
strictly prohibited. If you received this e-mail in error, please
contact the sender directly. 
 
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Frymire, Nathan
Sent: July 17, 2008 5:36 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Exterior Light Levels
 
Can anyone tell me where to modify exterior light levels in the detail
design screen (not a wizard).
 
Additionally, in this same format, how do you rotate the building axis
for 90.1 appendix G purposes?  
 
Thanks.
 
 
Nathan R. Frymire, LEED(r) A.P.                        
Mechanical Engineer
Burns & McDonnell
9400 Ward Parkway
Kansas City, MO 64114
 
Phone:  816-822-3900 ext 8513
Fax:  816-822-3423
 
         
www.burnsmcd.com <http://www.burnsmcd.com> 
 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080718/0d9600cb/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 3181 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080718/0d9600cb/attachment-0002.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1418 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080718/0d9600cb/attachment-0002.jpeg>
    
    
More information about the Equest-users
mailing list