[Equest-users] waterside economizer in eQuest
    Fred Porter 
    FPorter at archenergy.com
       
    Mon Jul 28 14:52:58 PDT 2008
    
    
  
No, that's not required. If the WSE-"Chiller" is listed with the chillers on a loop, DOE-2 will use it when conditions allow. "Conditions" include CHW temperature, so reset up of CHW if possible maximizes the modeled use of the WSE. 
>>> Brian Fountain <bfountain at greensim.com> 7/28/2008 2:12 PM >>>
Further to this -- you will likely need to set up your equipment 
controls to specify the water economizer chiller type leading in the 
winter (below a certain OA) and the regular chillers leading above a 
certain OA -- or based on a schedule.
Steve Mignogna wrote:
> You can set up a separate chiller of type "water economizer".  This 
> will attach to your CHW and CW Loops and will bypass the chiller and 
> circulate through your cooling tower when the outside air conditions 
> are acceptable for free cooling.
>
>
>
> On Fri, Jul 25, 2008 at 11:13 AM, Marcus Eliason <meliason at essexco.com 
> <mailto:meliason at essexco.com>> wrote:
>
>
>     Hello,
>
>     Can someone please explain the proper way to model a waterside
>     economizer in
>     eQuest?  I have found the option for a cooling tower with HX, but
>     this does
>     not seem to yield any results.
>
>     Thank you,
>
>     Marcus Eliason
>     Essex Engineering Corporation
>     404.365.9482
>     meliason at essexco.com <mailto:meliason at essexco.com>
>
>
>     _______________________________________________
>     Equest-users mailing list
>     http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org 
>     To unsubscribe from this mailing list send  a blank message to
>     EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
>     <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> -- 
> Steve Mignogna
> Atelier Ten
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org 
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
>   
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG. 
> Version: 7.5.524 / Virus Database: 270.5.5/1570 - Release Date: 7/24/2008 6:59 AM
>   
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org 
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080728/d340808a/attachment-0002.htm>
    
    
More information about the Equest-users
mailing list