Dan,
Thanks a lot for your feedback. It is really helpful for my projects.
Best,
Shaojie
--- On Fri, 11/7/08, Dan Russell <danr at engineeringinc.com> wrote:
From: Dan Russell <danr at engineeringinc.com>
Subject: RE: [Equest-users] DHW Input Rating
To: "shaojieworld2006 at yahoo.com" <shaojieworld2006 at yahoo.com>, "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Date: Friday, November 7, 2008, 6:19 PM
For standard office building 1 gal/person/day is about right for actual consumption. For DHW design of office buildings ASHRAE provides the chart below, which shows a recovery rate of 0.1 to 0.35 gal/person/hour. The difference depends on how much storage tank capacity you plan on having. Note that these values would be for peak loading and thus 1 gal/person/hour would result in far too much consumption than normal.
Thanks,
Dan Russell, EIT
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of eric wang
Sent: Wednesday, November 05, 2008 12:13 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] DHW Input Rating
Hi eQUEST Folks,
I used schematic design wizard for sizing DHW heater and found the default value of hot water use is 1 gal/person/day in the office building. After I changed the operation hour of main schedule for occupancy. The input rating kept the same. It seems to me that the unit of hot water use should be 1 gal/person/hour. Can anyone point out if my understanding is wrong?
Thanks a lot
Shaojie
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081110/8a623a3b/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 28026 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081110/8a623a3b/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 7994 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081110/8a623a3b/attachment-0001.jpg>
More information about the Equest-users
mailing list