[Equest-users] Multiple wall and floor types in same shell level
Gary.Schrader at tac.com
Gary.Schrader at tac.com
Wed Oct 29 09:01:25 PDT 2008
Probably the easiest way is to break it up into multiple shells, unless
somebody has found success doing it another way. Create one shell for
your slab-on-grade, and one shell on top of your ambient spaces. You can
create one shell on top of another by changing the "Z" coordinate in the
Wizard.
Same for the basement. One shell will be needed for the portion of the
basement with below-grade walls, and a 2nd shell for the above-grade
walls.
I have only ever had to do that once so there is probably some expertise
in the group that has an easier solution.
Good luck.
Gary Schrader
Engineer I
TAC
16011 College Blvd, Suite 212
Lenexa, KS 66219
Direct: +1
Fax: +1 913-469-0206
Mobile: +1 913-217-8068
Email: Gary.Schrader at tac.com
Web: www.tac.com <http://www.tac.com/>
Notice: This email message, together with any attachments, contains
information of TAC, which may be confidential, proprietary, copyrighted
and/or legally privileged. This email is intended solely for the use of
the individual or entity named on the message. If you are not the
intended recipient, and have received this message in error, please
immediately return by email and then delete it.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin
Felt
Sent: Wednesday, October 29, 2008 10:59 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Multiple wall and floor types in same shell
level
How do I model a shell floor where part is over a basement level that is
office space, part is slab on grade (the first floor is twice as large
as the second floor), and part of the floor is over ambient airspace.
Also, my basement is not fully below grade. Two of my walls are fully
above grade, the other two are below grade? How do I make that
distinction in eQuest?
Kevin A. Felt
Kevin A. Felt
Senior Technical Analyst
QA Designee
MaGrann Associates
856-722-9799
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081029/1fe3751f/attachment-0001.htm>
More information about the Equest-users
mailing list