[Equest-users] Rotating a single building in a campus setting
Karen Walkerman
kwalkerman at gmail.com
Mon Oct 6 11:17:57 PDT 2008
Under "building data" there is an AZIMUTH keyword. You can use this keyword
to rotate the whole building (you can do this in the parametric runs as
well).
--
Karen
On Mon, Oct 6, 2008 at 1:50 PM, Eric Allen Youngson <eyoungson at rmi.org>wrote:
> Sim list,
> I need to rotate a building (collection of shells) in a campus setting
> where there are are several buildings. I don't see any way to accomplish
> this parametrically so I am trying to change the azimuth of the shells
> individually. When I do this the shells rotate around the axis of the
> entire
> campus rather than around the center of the "building". There does not seem
> to be any central reference point for the shells since they all specify 0,0
> for x,y coordinates.
> Currently I am trying to reference the shells to their associated
> polygon.
> Any thoughts on this approach or other ideas on how to re-center the
> shells once the azimuth has been changed?
>
> Thanks,
>
> Eric
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081006/2568529e/attachment-0002.htm>
More information about the Equest-users
mailing list