[Equest-users] FCU with outside air fan
Yuvaraj Saravanan
Yuvaraj.Saravanan at arup.com
Mon Sep 22 21:05:26 PDT 2008
Hi All,
I am trying to model a residential unit served by a Fan coil unit (FCU). It has a separate outside air fan and exhaust fan operating 24/7. The fan coil unit is available to operate for all hours but should operate intermittently depending on the room load.
I tried modeling this by selecting a 4-pipe FCU and specified the exhaust and outside air at the thermal zone level. I made the FCU to operate intermittently by making the “Fan on mode” to be intermittent. By doing this, what I observed in the hourly report was:
1. FCU unit cycles intermittently as intended.
2. Exhaust fan operates continuously (24/7) (with the specified cfm) as intended.
3. However, the outside air cycles per the FCU.
•If the FCU is off, then OA cfm is zero
•If FCU supply air cfm < the OSA cfm specified at the zone level, then hourly OSA cfm matches the FCU supply air cfm
•If FCU supply air cfm > the OSA cfm specified at the zone level, then hourly OSA cfm matches the cfm specified at the zone level.
As mentioned before, I want my outside air to operate continuously with constant flow-rate. Can anyone suggest me a way to model this system?
Thanks in advance for your help!
Regards,
Yuvaraj
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
More information about the Equest-users
mailing list