[Equest-users] Equest-users Digest, Vol 17, Issue 3
Robert Yoakum
ryoakum at larseneng.com
Wed Aug 5 13:11:58 PDT 2009
You have to set your color printer as your default printer in the windows
control panel in order for eQuest to print in color. Then when your done you
can change it back to default to your black and white printer.
lol,
Robert Yoakum, LEED® AP
Designer
Larsen Engineering, Inc.
4662 Larwell Drive
Columbus, Ohio 43220
614-459-4002 (voice)
614-459-3124 (fax)
ryoakum at larseneng.com (e-mail)
This transmission may contain information that is privileged, confidential,
or exempt from disclosure under applicable law. If you are not the intended
recipient, you are hereby notified that any disclosure, copying,
distribution, or use of the information contained herein is strictly
prohibited. If you received this transmission in error, please contact the
sender and destroy the material in its entirety.
Email transmission cannot be guaranteed secure or error-free. Computer
viruses can be transmitted via email - check email and any attachments for
viruses. Larsen Engineering Inc. does not accept liability for errors or
omissions resulting from transmission or any damage caused by a virus
transmitted by this email.
On Wed, Aug 5, 2009 at 3:09 PM,
<equest-users-request at lists.onebuilding.org>wrote:
> Send Equest-users mailing list submissions to
> equest-users at lists.onebuilding.org
>
> To subscribe or unsubscribe via the World Wide Web, visit
>
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
> or, via email, send a message with subject or body 'help' to
> equest-users-request at lists.onebuilding.org
>
> You can reach the person managing the list at
> equest-users-owner at lists.onebuilding.org
>
> When replying, please edit your Subject line so it is more specific
> than "Re: Contents of Equest-users digest..."
>
> Today's Topics:
>
> 1. Printing Graphical Reports (Jeff Brown)
> 2. Re: Printing Graphical Reports (Jeremy McClanathan)
> 3. Re: Printing Graphical Reports (Dan Myers)
> 4. Re: Printing Graphical Reports (Charles Land)
> 5. LEED Related Modeling (ron lamarre)
> 6. DX/HW Dual-duct AHU (Muldoon, Kevin)
> 7. Re: DX/HW Dual-duct AHU (B. Fountain)
> 8. Chiller Type (Zareh, Hassan)
> 9. Re: Chiller Type (B. Fountain)
> 10. Pumps & Aux gas load (Crockett, Jim)
> 11. Re: Pumps & Aux gas load (Frank Hartley)
> 12. eQUEST Training October 13 & 14 (Lee DeBaillie)
> 13. Heat recovery from the condenser to heating coil and heat
> recovery on air evacuation using a DX system with water-glycol
> (Gal, Amandine)
>
>
> ---------- Forwarded message ----------
> From: Jeff Brown <jbrown at WJO.com>
> To: "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Date: Tue, 4 Aug 2009 16:52:03 -0400
> Subject: [Equest-users] Printing Graphical Reports
>
> All,
>
>
>
> Is the fact I cannot print graphical reports in color unique to me? All
> parameters are set to print in color but sent either to a .pdf file or a
> printer the files are black and white.
>
>
>
> The 2D Chart Control Properties, when modified for 3D view, etc., also
> revert to default before the document is printed.
>
>
>
> Can anyone offer me some help with this?
>
>
>
> Thank you!
>
>
>
> JJB
>
>
>
> *Jeffrey J. Brown*
>
> Operations Manager
>
> *The Controls Group*
>
> *W.J. O'Neil Company*
>
> jbrown at wjo.com
>
>
>
>
> ---------- Forwarded message ----------
> From: Jeremy McClanathan <jmcclanathan at CDiengineers.com>
> To: 'Jeff Brown' <jbrown at WJO.com>, "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Date: Tue, 4 Aug 2009 16:26:16 -0700
> Subject: Re: [Equest-users] Printing Graphical Reports
>
> I had the same problem in the past. The solution for me was to set the
> color printer as my default printer.
>
> Jeremy
>
>
>
> *From:* Jeff Brown [mailto:jbrown at WJO.com]
> *Sent:* Tuesday, August 04, 2009 1:52 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Printing Graphical Reports
>
>
>
> All,
>
>
>
> Is the fact I cannot print graphical reports in color unique to me? All
> parameters are set to print in color but sent either to a .pdf file or a
> printer the files are black and white.
>
>
>
> The 2D Chart Control Properties, when modified for 3D view, etc., also
> revert to default before the document is printed.
>
>
>
> Can anyone offer me some help with this?
>
>
>
> Thank you!
>
>
>
> JJB
>
>
>
> *Jeffrey J. Brown*
>
> Operations Manager
>
> *The Controls Group*
>
> *W.J. O'Neil Company*
>
> jbrown at wjo.com
>
>
>
> This email message, including any attachments, is for the sole use of the
> intended recipient and may contain confidential, proprietary, and/or
> privileged information, as well as content subject to copyright and other
> intellectual laws. If you are not the intended recipient, you may not
> disclose, use, copy, or distribute the email message or its attachments. If
> you believe you have received this email message in error, please contact
> the sender by reply email, immediately delete this email and destroy copies.
>
>
> ---------- Forwarded message ----------
> From: "Dan Myers" <dmyers at rnm-engineers.com>
> To: "'Jeff Brown'" <jbrown at WJO.com>, <equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 07:34:07 -0400
> Subject: Re: [Equest-users] Printing Graphical Reports
>
> We’ve had the same problem in our office. Even with a color printer as our
> default, it would still print in black and white (even though it previews in
> color). We’ve had to make our PDF writer our default printer and print to a
> PDF file.
>
>
>
> Dan Myers
>
> RNM Engineers
>
> 409 North Haywood Street
>
> Waynesville, NC 28786
>
> Tel: 828-456-9851 ext. 110
>
> Fax: 828-456-6205
>
> dmyers at rnm-engineers.com
>
> P Save resources. Please print with discretion.
>
>
> ------------------------------
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jeff Brown
> *Sent:* Tuesday, August 04, 2009 4:52 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Printing Graphical Reports
>
>
>
> All,
>
>
>
> Is the fact I cannot print graphical reports in color unique to me? All
> parameters are set to print in color but sent either to a .pdf file or a
> printer the files are black and white.
>
>
>
> The 2D Chart Control Properties, when modified for 3D view, etc., also
> revert to default before the document is printed.
>
>
>
> Can anyone offer me some help with this?
>
>
>
> Thank you!
>
>
>
> JJB
>
>
>
> *Jeffrey J. Brown*
>
> Operations Manager
>
> *The Controls Group*
>
> *W.J. O'Neil Company*
>
> jbrown at wjo.com
>
>
> size=2 width="100%" align=center>
>
> *Total Control Panel*
>
> Login <https://asp-4.reflexion.net/login?domain=rnm-engineers.com>
>
> To: dmyers at rnm-engineers.com<https://asp-4.reflexion.net/address-properties?aID=54337127>
>
> From: equest-users-bounces at lists.onebuilding.org<https://asp-4.reflexion.net/address-properties?aID=54601063>
>
> Remove<https://asp-4.reflexion.net/FooterAction?ver=1&un-wl-sender-address=1&rID=54337127&aID=54601063>this sender from my allow list
>
> *You received this message because the sender is on your allow list.
> *
>
>
>
>
> ---------- Forwarded message ----------
> From: Charles Land <cland at geo-marine.com>
> To: "dmyers at rnm-engineers.com" <dmyers at rnm-engineers.com>, 'Jeff Brown'
> <jbrown at WJO.com>, "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 07:20:08 -0500
> Subject: Re: [Equest-users] Printing Graphical Reports
>
> You have to go under your start menu, choose your printer preferences and
> change to color through there.
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Dan Myers
> *Sent:* Wednesday, August 05, 2009 7:34 AM
> *To:* 'Jeff Brown'; equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Printing Graphical Reports
>
>
>
> We’ve had the same problem in our office. Even with a color printer as our
> default, it would still print in black and white (even though it previews in
> color). We’ve had to make our PDF writer our default printer and print to a
> PDF file.
>
>
>
> Dan Myers
>
> RNM Engineers
>
> 409 North Haywood Street
>
> Waynesville, NC 28786
>
> Tel: 828-456-9851 ext. 110
>
> Fax: 828-456-6205
>
> dmyers at rnm-engineers.com
>
> P Save resources. Please print with discretion.
>
>
> ------------------------------
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Jeff Brown
> *Sent:* Tuesday, August 04, 2009 4:52 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Printing Graphical Reports
>
>
>
> All,
>
>
>
> Is the fact I cannot print graphical reports in color unique to me? All
> parameters are set to print in color but sent either to a .pdf file or a
> printer the files are black and white.
>
>
>
> The 2D Chart Control Properties, when modified for 3D view, etc., also
> revert to default before the document is printed.
>
>
>
> Can anyone offer me some help with this?
>
>
>
> Thank you!
>
>
>
> JJB
>
>
>
> *Jeffrey J. Brown*
>
> Operations Manager
>
> *The Controls Group*
>
> *W.J. O'Neil Company*
>
> jbrown at wjo.com
>
>
>
> <hr size=2 width="100%" align=center>
>
> *Total Control Panel*
>
> Login <https://asp-4.reflexion.net/login?domain=rnm-engineers.com>
>
> To: dmyers at rnm-engineers.com<https://asp-4.reflexion.net/address-properties?aID=54337127>
>
> From: equest-users-bounces at lists.onebuilding.org<https://asp-4.reflexion.net/address-properties?aID=54601063>
>
> Remove<https://asp-4.reflexion.net/FooterAction?ver=1&un-wl-sender-address=1&rID=54337127&aID=54601063>this sender from my allow list
>
> *You received this message because the sender is on your allow list.*
>
>
>
>
> ---------- Forwarded message ----------
> From: ron lamarre <lamarre_arch at yahoo.com>
> To: equest-users at lists.onebuilding.org
> Date: Wed, 5 Aug 2009 06:41:47 -0700 (PDT)
> Subject: [Equest-users] LEED Related Modeling
> Hi to all:
>
> I'd like to see if anyone else has run into the following issues and/or can
> assist with the resolution.
>
> 1. How does one model an ERV for one zone on a multi-zone PVVT system.
> ie: one constant-volume RTU with four zones with change-over bypass
> dampers. The ERV is placed in the supply duct to one zone and is controlled
> with demand control sensors. It appears in eQuest, the DCV controls only
> work system wide.
>
> 2. We're using a low-temp condensing DHW to heat potable water as well as
> two split system AHUs. There does not seem to be a selection for this
> type of DHW under the HVAC heating coil options; however, there is a
> condensing boiler option. When we reduce the water load (40% DHW reduction)
> and input the low temp (110F) and high efficiency of the actual DHW, we are
> seeing a 58% saving in fuel (gas) over the 80% Et baseline. Does this sound
> correct?
>
> 3. We have tsak lighting in each office/workspace of this commercial
> office building for individual occupant controllability. We included the
> task lighting power density in the Space-by-Space allowable W/SF for the
> baseline. In the proposed model, the task lighting power is added to the
> fixed lighting power for the total lighting W/SF. Should the power for the
> task lighting also be added to the baseline as a process load?
>
>
> Thanks for your help.
>
> *Ron Lamarre, AIA, NCARB*
> Architect - *LEED AP*
>
> *L A M A R R E A R C H I T E C T S*
> 3 Hoyt Circle
> Atkinson NH 03811
>
>
>
> ---------- Forwarded message ----------
> From: "Muldoon, Kevin" <kmuldoon at ameresco.com>
> To: "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 11:21:41 -0400
> Subject: [Equest-users] DX/HW Dual-duct AHU
>
> I am trying to model a HVAC system that is a multi-zone AHU (one AHU for
> the building (1 floor)) and it has HW heat with DX cooling but it is also a
> double duct system. I need some help on getting around to model this
> system.
>
>
>
> Thanks
>
> Kevin Muldoon
>
> Mechanical Engineering Co-op
>
> [image: cid:710031015 at 04062009-29F5]
>
> 9000 Wessex Place Suite #304
>
> Louisville, Kentucky 40222
>
> P 502 420 1980
>
> F 502 420 1998
>
> C 502 552 5930
>
> E kmuldoon at ameresco.com
>
>
>
> **************************************************************************************
> NOTE: This e-mail may contain PRIVILEGED and CONFIDENTIAL information and is intended only for the use of the specific individual(s) to which it is addressed. If you are not an intended recipient of this e-mail, you are hereby notified that any unauthorized use, dissemination or copying of this e-mail or the information contained in it or attached to it is strictly prohibited. If you have received this e-mail in error, please delete it and immediately notify the person named above by reply e-mail. Thank you.
> **************************************************************************************
>
>
>
>
> ---------- Forwarded message ----------
> From: "B. Fountain" <bfountain at greensim.com>
> To: "Muldoon, Kevin" <kmuldoon at ameresco.com>
> Date: Wed, 5 Aug 2009 11:28:51 -0400 (EDT)
> Subject: Re: [Equest-users] DX/HW Dual-duct AHU
> Sounds like a packaged multizone system to me -- have a look at the system
> diagram in the DOE2 help file to see if it meets your requirements. It is
> even available in the DD wizard.
>
> > I am trying to model a HVAC system that is a multi-zone AHU (one AHU for
> > the building (1 floor)) and it has HW heat with DX cooling but it is also
> > a double duct system. I need some help on getting around to model this
> > system.
> >
> > Thanks
> > Kevin Muldoon
> > Mechanical Engineering Co-op
> > [cid:image001.jpg at 01CA15BE.E84BED20]
> > 9000 Wessex Place Suite #304
> > Louisville, Kentucky 40222
> > P 502 420 1980
> > F 502 420 1998
> > C 502 552 5930
> > E kmuldoon at ameresco.com<mailto:kmuldoon at ameresco.com>
> >
> >
> >
> **************************************************************************************
> > NOTE: This e-mail may contain PRIVILEGED and CONFIDENTIAL information and
> > is intended only for the use of the specific individual(s) to which it is
> > addressed. If you are not an intended recipient of this e-mail, you are
> > hereby notified that any unauthorized use, dissemination or copying of
> > this e-mail or the information contained in it or attached to it is
> > strictly prohibited. If you have received this e-mail in error, please
> > delete it and immediately notify the person named above by reply e-mail.
> > Thank you.
> >
> **************************************************************************************
> >
> _______________________________________________
> > Equest-users mailing list
> > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> > To unsubscribe from this mailing list send a blank message to
> > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> >
>
>
>
>
>
> ---------- Forwarded message ----------
> From: "Zareh, Hassan" <Hassan.Zareh at stantec.com>
> To: <equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 09:34:29 -0600
> Subject: [Equest-users] Chiller Type
> Hi,
> I'm modeling a high rise residential building. The proposed building has
> one centrifugal chiller but based on ASHRAE, the reference building should
> have two rotary screw chillers, but eQuest doesn't allow me to have
> different type of chillers in parametric run. In parametric run when I try
> to change the type of the chiller, the program crashes. Any comment?
>
> Thanks in advance.
>
> *Hassan Zareh, M.Eng., P.Eng., LEED® AP*
> Project Engineer
> Stantec Consulting Ltd.
> 100 - 401 Wellington Street West
> Toronto ON M5V 1E7
> Ph: (416) 598-7642
> Fx: (416) 596-6680
> hzareh at stantec.com
> *stantec*.com <http://www.stantec.com/>
>
> The content of this email is the confidential property of Stantec and
> should not be copied, modified, retransmitted, or used for any purpose
> except with Stantec's written authorization. If you are not the intended
> recipient, please delete all copies and notify us immediately.
>
> ü Please consider the environment before printing this email.
>
>
> ---------- Forwarded message ----------
> From: "B. Fountain" <bfountain at greensim.com>
> To: "Zareh, Hassan" <Hassan.Zareh at stantec.com>
> Date: Wed, 5 Aug 2009 12:09:51 -0400 (EDT)
> Subject: Re: [Equest-users] Chiller Type
> One possible solution would be to define both refrigeration plants in the
> baseline model and then create two Equipment Controls -- one for the
> proposed building with only the single centrifugal chiller enabled and one
> for the ASHRAE reference with the 2 screw chillers enabled (without the
> centrifugal). In the parametric run for the chilled water loop you can
> change the Cool Equipment Control selection under loop control.
>
> Check the PS-H report for all chillers to see that the strategy worked.
>
>
> > Hi,
> > I'm modeling a high rise residential building. The proposed building has
> > one centrifugal chiller but based on ASHRAE, the reference building
> should
> > have two rotary screw chillers, but eQuest doesn't allow me to have
> > different type of chillers in parametric run. In parametric run when I
> try
> > to change the type of the chiller, the program crashes. Any comment?
> >
> > Thanks in advance.
> >
> > Hassan Zareh, M.Eng., P.Eng., LEED® AP
> > Project Engineer
> > Stantec Consulting Ltd.
> > 100 - 401 Wellington Street West
> > Toronto ON M5V 1E7
> > Ph: (416) 598-7642
> > Fx: (416) 596-6680
> > hzareh at stantec.com
> > stantec.com <http://www.stantec.com/>
> >
> > The content of this email is the confidential property of Stantec and
> > should not be copied, modified, retransmitted, or used for any purpose
> > except with Stantec's written authorization. If you are not the intended
> > recipient, please delete all copies and notify us immediately.
> >
> > ü Please consider the environment before printing this email.
> > _______________________________________________
> > Equest-users mailing list
> > http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> > To unsubscribe from this mailing list send a blank message to
> > EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> >
>
>
>
>
>
> ---------- Forwarded message ----------
> From: "Crockett, Jim" <Jcrockett at nexant.com>
> To: <equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 10:01:07 -0700
> Subject: [Equest-users] Pumps & Aux gas load
>
> Any idea what type of gas loads would show up in the “Pumps & Aux”
> category? The BEPS report shows 69 therms of Natural Gas consumption in the
> “Pumps & Aux” category. Have combed through the model, but can’t find where
> this is coming from. I checked the meter, and no direct loads have been
> assigned to this category. Any thoughts?
>
>
>
> Thanks,
>
>
>
>
>
> Jim Crockett, P.E.
>
>
>
> Senior Project Engineer
>
> Energy & Carbon Management
>
> Nexant, Inc.
>
> 4021 S. 700 E., Suite 250
>
> Salt Lake City, Utah 84107
>
>
>
> (801) 639-5603 - phone
>
> (801) 266-4786 - fax
>
>
>
>
> ---------- Forwarded message ----------
> From: Frank Hartley <fhartley at dynamix-ltd.com>
> To: "Crockett, Jim" <Jcrockett at nexant.com>, "
> equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 13:06:04 -0400
> Subject: Re: [Equest-users] Pumps & Aux gas load
>
> Equest includes furnace pilot lights in this category. Check the unitary
> power tab under your system’s heating and look for Furnace Fuel Auxiliary.
>
>
>
> *From:* equest-users-bounces at lists.onebuilding.org [mailto:
> equest-users-bounces at lists.onebuilding.org] *On Behalf Of *Crockett, Jim
> *Sent:* Wednesday, August 05, 2009 1:01 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Pumps & Aux gas load
>
>
>
> Any idea what type of gas loads would show up in the “Pumps & Aux”
> category? The BEPS report shows 69 therms of Natural Gas consumption in the
> “Pumps & Aux” category. Have combed through the model, but can’t find where
> this is coming from. I checked the meter, and no direct loads have been
> assigned to this category. Any thoughts?
>
>
>
> Thanks,
>
>
>
>
>
> Jim Crockett, P.E.
>
>
>
> Senior Project Engineer
>
> Energy & Carbon Management
>
> Nexant, Inc.
>
> 4021 S. 700 E., Suite 250
>
> Salt Lake City, Utah 84107
>
>
>
> (801) 639-5603 - phone
>
> (801) 266-4786 - fax
>
>
>
>
> ---------- Forwarded message ----------
> From: Lee DeBaillie <ldebaillie at ecw.org>
> To: "equest-users at lists.onebuilding.org" <
> equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 10:31:27 -0700
> Subject: [Equest-users] eQUEST Training October 13 & 14
>
> eQUESTers,
>
>
>
> The Energy Center of Wisconsin will be sponsoring Introductory and
> Intermediate eQUEST training on October 13th & 14th 2009 in Wauwatosa,
>
> Wisconsin - just outside of Milwaukee.
>
>
>
> The first day will provide instruction on early design modeling approaches
> using the SD and DD wizards. The second day will focus on more in-depth
> modeling using the eQUEST detailed interface.
>
>
>
> Follow the link below for details, training agenda, and to register
> on-line.
>
> http://www.ecw.org/university/ecuevent.php?ecuid=232
>
>
>
> Registration is $289/day or $469 for both days.
>
>
>
> Lee DeBaillie
>
> Energy Center of Wisconsin
>
>
>
>
> ---------- Forwarded message ----------
> From: "Gal, Amandine" <Amandine.Gal at snclavalin.com>
> To: <equest-users at lists.onebuilding.org>
> Date: Wed, 5 Aug 2009 14:15:52 -0400
> Subject: [Equest-users] Heat recovery from the condenser to heating coil
> and heat recovery on air evacuation using a DX system with water-glycol
> Dear Equest users,
>
> I just arrived to Canada and I have to make a model of a building in
> Montréal for LEED. I would like to know if Equest has the features to model
> the HVAC systems of this building.
>
> To reduce the heating consumption, we would like to take the heat from the
> condensers of the different chillers to use it to heat the heating coils of
> the ventilation system. Moreover, we would like to recover the heat for the
> air evacuation with direct expansion system to heat the condenser.
>
> Do you think that is possible to model it with EQuest? and if yes, ( I hope
> because if not, I have to model it with EnergyPlus but it will be quite more
> complicated), how to do it?
>
> Thank you in advance.
>
> Regards
>
>
> *Amandine Gal*
>
> Spécialiste en ingénierie
>
> Division Transport, Infrastructures et Bâtiment
>
>
>
> *SNC-Lavalin inc.*
>
> 8000 boul. Décarie, 3e étage
>
> Montréal (Québec)
>
> Canada H4P 2S4
>
> Téléphone: 514-735-5651 poste 2346
>
> Télécopieur: 514-737-7988
>
> Courriel: *amandine.gal*@snclavalin.com
>
> www.snclavalin.com
>
>
> _______________________________________________
> Equest-users mailing list
> Equest-users at lists.onebuilding.org
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090805/56d28fd9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2452 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090805/56d28fd9/attachment.jpeg>
More information about the Equest-users
mailing list