[Equest-users] ASHRAE 90.1 baseline for pool dehumidifier

Jacob Goodman jacobg at lseng.com
Thu Aug 13 09:05:05 PDT 2009


I was wondering if anyone has had experience modeling a pool facility 
for LEED and could recommend what is a "baseline" dehumidifier system 
that complies with AHSRAE 90.1. One though I had is 100% outside air 
system with 50% effective sensible heat recovery to satisfy AHSRAE 90.1 
G3.1.2.10. One dealer I talk to claimed this was "industry standard".

However, if my proposed dehumidifier saves energy by reducing the amount 
of OA that needs to be reheated (it should drop to about 30% OA) will I 
run into trouble with AHSRAE 90.1 G3.1.2.5 that says I need to have the 
same min. OA in the baseline and proposed?

Jacob Goodman , LEED AP


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090813/ce8ac265/attachment.htm>


More information about the Equest-users mailing list